Hey team! I have a single-phase output UPS that I need to power a three-phase input DC supply. It's going to cost me way too much to replace either of the units. How practical would it be for me to add a 1-phase to 3-phase converter between my UPS and DC supply? I know I stand to lose ~1/3 capacity on the converter; are there any other considerations I'm overlooking? Do any of you have a good schematic that shows standard converter electronics?
The intent is to go with an off-the-shelf item.
The Ultimate Problem I need to solve is as stated: I have a 1 phase output from my UPS, but it needs to supply a three phase load.
Plan: buy a 1-to-3 phase converter to solve the problem. Having never used one before I was looking for a circuit diagram to better understand what I'm putting into my system. Also looking for any practical advice on using a 1-to-3 phase converter - any considerations I might be overlooking.
Thanks!
upsers
On 12/12/2020 6:42 PM, Mitchel said: any considerations I might be overlooking.
any considerations I might be overlooking.
Voltage. 3 Phase is 120 degrees separated whereas your single phase voltage will translate directly through the converter. If you were in Australia for example, on 230V mains you'd normally have a nominal 415V three phase. Using a converter you get 230V 3 phase. You'll need to look carefully at the output of the converter to make sure it's what you really need. Additionally, the cheap-mid market converters tend to have really poor input power factor with direct rectified mains rather than using a PFC boost converter, so you'll want to make sure the UPS is happy with that.
On 5/1/2021 12:35 PM, Patricia said: What's the probability that it will work completely fine without any issues in it.
What's the probability that it will work completely fine without any issues in it.
About the same probability you'd come back after 24 hours and insert a spam link in your post. Oh, gee. Look at that!