  • dkleber

    We get alerted to these about once a month but I can't see what's triggering it, there isn't much on the UPS. Any idea on what I can do to stop these errors? 

    Quick Status
     
    Load in Watts Battery Capacity
     
     
     
     
     
     
    56.4 %
     
     
     
     
     
    100.0 %
     
     
    Input Voltage: 116.5 | 115.9 | 115.8 VAC[Phase L1 | L2 | L3]
    Output Voltage: 120.8 | 120.9 | 121.0 VAC[Phase L1 | L2 | L3]
     
    Runtime Remaining: 41min
    Last Battery Transfer: Due to software command or UPS's test control
     
     
         
     
    Recent UPS Events
      Date Time Event
      12/05/2018 08:21:06 UPS: Passed a self-test.
  • wpasquil

    Hi,

    The event indicates the UPS passed a self-test. That is a good thing. The UPS will run a self-test to verify the batteries can sustain the load. 

    If you have other concerns or further questions please contact APC by Schneider Electric 3 phase UPS support at 1-800-555-2725 then option 4