UPS Symmetra PX 250-500 SNMP Walk

Subscribe to RSS
  • daniel75

    Hi Community Expert,

    We have a site install with a UPS Symmetra PX 250 - 500 (400kW).

    When we perform a SNMP Walk with our powernetmib426, we found out there are few OID points information was confusing. Can we get the require information below from the SNMP Walk or we choose the wrong OID point. Please refer to the table below:- 

    S/N

    Description

    Attribute Name

    OID

    SNMP WALK

    Return value

    Remarks

    1

    Bypass system frequency

    upsAdvInputBypassNominalFrequency

    .1.3.6.1.4.1.318.1.1.1.3.2.8.0

    NA

    Available in MIB file,

    Not Available in SNMP WALK Results,

    Available in equipment display

     

    2

    Bypass current phase 1, 2 & 3

     

     

     

    Not Available in MIB file,

    Not Available in SNMP WALK Results,

    Available in equipment display

     

    3

    Bypass system voltage phase 1, 2 & 3

    upsAdvInputBypassNominalVoltage

    .1.3.6.1.4.1.318.1.1.1.3.2.9.0

    NA

    Available in MIB file,

    Not Available in SNMP WALK Results,

    Available in equipment display

     

    4

    Bypass system total active power

    upsAdvInputBypassTotalActivePower

    .1.3.6.1.4.1.318.1.1.1.3.2.14.0

    NA

    5

    Bypass system total apparent power

    upsAdvInputBypassTotalApparentPower

    .1.3.6.1.4.1.318.1.1.1.3.2.13.0

    NA

    6

    The battery pack temperature measured in 10ths of degree Celcius

    upsHighPrecBatteryPackTemperature

    .1.3.6.1.4.1.318.1.1.1.2.3.10.2.1.5

    NA

    Available in MIB file,

    Not Available in SNMP WALK Results,

    Available in equipment display.

     

    Please advise which is the right attribute for “Power system temperature power module”. Refer to the T&C report and UPS equipment display as attached.

     

    7

    The battery frame/cabinet temperature in tenths of degrees celsius.

    upsDiagBatteryFrameTemperature

    .1.3.6.1.4.1.318.1.1.1.13.3.2.1.9

    NA

    8

    The battery frame/cabinet temperature in tenths of degrees celsius.

    upsDiagBatteryTemperature

    .1.3.6.1.4.1.318.1.1.1.13.3.4.1.5

    NA

    9

    The current state of the UPS inverter

    upsBasicSystemInverterStatus

    .1.3.6.1.4.1.318.1.1.1.4.1.5.0

    NA

    Available in MIB file,

    Not Available in SNMP WALK Results

     

    10

    The general status of the power factor correction

    upsBasicSystemPFCStatus

    .1.3.6.1.4.1.318.1.1.1.4.1.6.0

    NA

    11

    The measured battery power in kW.

    upsAdvBatteryPower

    .1.3.6.1.4.1.318.1.1.1.2.2.16.0

    0

    Available in MIB file,

    Not Available in SNMP WALK Results,

    Available in equipment display

     

      