removing the static switch bypass module.

Discussion in Data Center & Facility 3 Phase UPS started by Alberto , 7/18/2018 7:33 AM
Login to follow, share, and participate in this space.
Not a member?Join now
Posted in: General

removing the static switch bypass module.

Subscribe to RSS
  • Beto

    hello everybody.

    I would like to know what will happen if I remove static switch bypass module when the ups( symmetra px 160) is on?

  • kashif

    Nothing will happen as far as ups is online. If for that instant if problem occurs in utility and ups tries to go to by pass and at time if static bypass is not avb it will drop the load.

  • Beto

    thank you so much for your help.