MEGA GALAXY 5500

Subscribe to RSS
  • eslamsaad88

    I HAVE ERROR MESSAGE SAYS EXTERNAL COMMUNICATION ERROR AND HAVE ERROR CODE 7-5-1ERROR PHOTO

    Attachments
  • samanpriya

    We are also having same issue with Galaxy 5500 UPS Kindly advice.............

  • s.v.s

    External communication fault typically indicates a CAN communication fault between the installed UPS units, assuming there are more than one unit on site connected in parallel. If the UPS is a standalone unit then it could also be a configuration issue (i.e. unit is set to parallel mode). For in-depth troubleshooting and potential service I recommend reaching out to your local APC tech support as you might want an authorized service engineer to assess the UPS and installation.

Page 1 of 1 (3 items)