Generator no longer running scheduled test

Subscribe to RSS
  • Hanson2433

    We have a APC InfraStuxure ATS swith on a Cummins generator (125DSHAE-6409) that quit running the weekly test that are scheduled. The event only shows last test from a couple of weeks ago and no alarms. Have tried changed scheduled test today about 3 times and count down to time of start, but doesn't do anything. Again no alarms or events.

    125DSHAE-6409

  • voidstar

    Just a shot in the dark but check to see if the web interface is keeping time correctly and also try a reset to defaults.

  • Hanson2433

    The clock is keeping correct time. What would I set to defaults? Whole system?

  • voidstar

    Save the config.ini file first -- it contains all configuration parameters.

    Also, restart the network management card if you haven't already done so. The network management card runs the scheduled generator tests.

    Can you manually run a generator test?

  • Hanson2433

    I did just kill the power to make sure the generator kicks in and it did. Thanks

  • Hanson2433

    Yes it manually starts fine, but wasn't sure about power outage so I threw the main breaker and it worked fine.