Can a 3-phase APC SYMSTRF3I still power up on single phase supply.

Discussion in Data Center & Facility 3 Phase UPS started by Dhile , 11/15/2010 3:18 AM
Login to follow, share, and participate in this space.
Not a member?Join now
Posted in: General

Can a 3-phase APC SYMSTRF3I still power up on single phase supply.

Subscribe to RSS
  • Dhile

    We moved our 3-phase APC SYMSTRF3I UPS to another building, which only has a single phase supply currenlty. Is it possible to power this UPS with just a single phase (UPS will only be supporting 2 servers). If possible could you please let me know how I could connect and power up the UPS. Thanks

    apc
  • JoeMomma

    SYMSTRF3I can be used in either 3:1 or 1:1 mode. The SYPM power module is universal and the 3:1 chassis allows for full current to pass through the AC_IN1 bus.

    In 1:1 mode, acceptable nominal input (Hot-Neutral-Ground) would be 220/230/240 as you would expect.

    And the full *3:1* user manual can be found here:
    http://www.apcmedia.com/salestools/ASTE-6Z8LBY_R0_EN.pdf

    The full *1:1* user manual can be found here:
    http://www.apcmedia.com/salestools/ASTE-6Z8L9K_R0_EN.pdf

  • zzm313

    Hi Matt- thanks for this info.  As you said:SYMSTRF3I can be used in either 3:1 or 1:1 mode.How can I input a single phase supply(used in  1:1 )?Thanks!