Galaxy 3000 charger fault

Discussion in Data Center & Facility 3 Phase UPS started by Luis , 4/14/2017 12:16 PM
Login to follow, share, and participate in this space.
Not a member?Join now
Posted in: General

Galaxy 3000 charger fault

Subscribe to RSS
  • Lhfelice

    Hello all,

    We have a galaxy 3000 ups that after a restart return charger fault and the battery cb goes off after 5 to 10 seconds of the startup.

    The batteries are fully charged, each one reads between 13.3 and 13.5, the whole group reads 320v.

    Any idea I appreciate.

  • wpasquil
    This discussion is marked as answered

    Luis,

    I asked our Galaxy support team and they replied 

    Most likely he has an open battery or connection in his battery string.

    They recommend you call into 3 phase Tech Support 1-401-789-5735 when prompted press 2 then 4 and then 4 again for 3 phase support.

  • scort

    You need to measure the voltage of each battery separately, necessarily with a small load of 2-5 watts

Page 1 of 1 (3 items)