error code 1-1-5 for galaxy 5500 120kva

Discussion in Data Center & Facility 3 Phase UPS started by sara , 2/12/2016 5:59 PM
Login to follow, share, and participate in this space.
Not a member?Join now
Posted in: General

error code 1-1-5 for galaxy 5500 120kva

Subscribe to RSS
  • ramsystem

    We have a 120 kva ups , the device is off when I on Q4s key this error appear:

    CC board fault

    CH board valid

    Error code 1-1-5

    Please help me what can I do?

  • eng.tohidi_at_gmail.com

    Hi Sara,

    Check two flat cables on MIZN board for loss connection:

    1- Flat cable between MIZN and DALIN (XML10-XMB16)

    2- Flat cable between MIZN and ALIN (XML09-XMA07)

    If they are ok i think you must replace MIZN board. After replacement you need UPS TUNER software to setup UPS.

  • elsafty

    Dear,

    could you help me with the pin to pin of the cables that wire 2 parallel galaxy 5000

    Attachments
  • mmiole

    Please anyone can help me... this the error no exact detail only Und. Msg. please help!