Hello,
I have a SRT5KXLI 5000VA with UPS Network Management Card 2 pre-installed. I have snmp enabled on it and I need to get the data of Energy Usage using SNMP. However, I couldn't find the corresponding OID in the MIB file. Does anyone know of this OID or is there any other way to get this data from the UPS using SNMP.
The data I am talking about is listed on this page.
Any help or ideas please?
Alright,
Found it.
Total Energy Usage OID
.1.3.6.1.4.1.318.1.1.1.4.3.6.0