How to find mgmt card model of insalled card ?

Discussion in UPS Management Devices & PowerChute Software started by Simon , 9/24/2020 6:45 PM
Login to follow, share, and participate in this space.
Not a member?Join now
Announcement 

Please review Schneider Electric Knowledge Base articles for assistance with most technical support questions.  http://www.apc.com/us/en/faqs

Posted in: General

How to find mgmt card model of insalled card ?

Subscribe to RSS
  • slaurendeau

    Hi, I don't have much experience with APC products or UPS in general but I'm looking for an easy way to remotely figure out which management card is installed in a Galaxy 5000 60 KVA.

    I have access to Struxtureware Data center Expert but I still can't figure which model it is.

    Looking to download the corresponding PowerNet Mib file once I have the model number.

    any help would be appreciated!

  • wpasquil

    Hi,

    It will depend on the card and firmware. Log in to the card and go to About - Network. You will see the model and firmware info. 

  • slaurendeau

    I don't see "About - Network" anywhere, but I found "About- UPS"  with this info :

     

    About your UPS / STS

     GALAXY 5000 60 kVA  
    UPS / STS Name :
    GALAXY 5000 60 kVA
    UPS / STS Firmware revision :
    KD.GDENB1S300IC303
     Network Management Card  
    Firmware revision : KD (SN 49er35533)
  • APC_Gavan

    I believe you have a pre-APC card, the MGE SNMP Web Card - 66074 (KD revision)

    https://www.se.com/ww/en/product/66074/mge-snmp-web-card/ 

    The below FAQ has a video that you can use to confimr:

    https://www.se.com/ww/en/faqs/FA281356/

    -Gavan