Loading ...

Powerchute Business not showing multiple UPS | UPS Management Devices & PowerChute Software

Home » Spaces » UPS Management Devices & PowerChute Software » discussion » General » Powerchute Business not showing multiple UPS

Powerchute Business not showing multiple UPS

Discussion in UPS Management Devices & PowerChute Software started by Nate , 8/13/2019 4:01 PM
Login to follow, share, and participate in this space.
Not a member?Join now
Announcement 

Please review Schneider Electric Knowledge Base articles for assistance with most technical support questions.  http://www.apc.com/us/en/faqs

Posted in: General

Powerchute Business not showing multiple UPS

Subscribe to RSS
  • nate_c

    I recently installed PowerChute Business Edition on a VM to monitor 2 Smart-UPS 1500 via USB. But for some reason only 1 is showing up? Is there any way to get both to show up in the software?

    I installed Tripp-Lite software and it's detecting both

  • wpasquil

    Hi,

    When running PCBE the Agent talks with the UPS and represents the UPS. You can only run a single Agent on a system at one time. If you would like to view 2 system from a single system you would need to connect each UPS to different compatible OS and install the Agent on each OS. Then you can open the web interface to each Agent from a single system.

    Another option is to view each Agent using and SNMP agent. 

Page 1 of 1 (2 items)
Choose your language:  
powered by Communifire
Version 6.0.7263.6123