PowerChute behavior during battery

Discussion in UPS Management Devices & PowerChute Software started by me , 1/2/2019 6:47 AM
Login to follow, share, and participate in this space.
Not a member?Join now
Announcement 

Please review Schneider Electric Knowledge Base articles for assistance with most technical support questions.  http://www.apc.com/us/en/faqs

  • baseball
    me
    New Member New Member
    me 1/2/2019 6:47 AM

    I will soon install SRT3000xli + 2 battery pack SRT96BP + AP9631. I have a question about PowerChute behaviour during calibration. How it will consider the status of UPS? It will see that UPS is "on battery"? If I set a delay time for "UPS on battery" event, will PowerChute shutdown the system even if there is no AC fault? I would like to avoid that PCNS will shutdown the servers during calibration.

  • wpasquil
    Bill
    =S= Representative
    Bill 1/2/2019 6:20 PM (in response to me)

    Hello,

    PowerChute will ignore the calibration test so the server/s will continue to run normally. 