Connection powerchute to management card using non standard http/https ports

Discussion in UPS Management Devices & PowerChute Software started by Fabio , 8/1/2018 11:02 AM
Login to follow, share, and participate in this space.
Not a member?Join now
Announcement 

Please review Schneider Electric Knowledge Base articles for assistance with most technical support questions.  http://www.apc.com/us/en/faqs

  • flaserra
    Fabio
    Novice Novice
    Fabio 8/1/2018 11:02 AM

    Hello

    I need to configure a Powerchute windows client to connect to a management card using http/https protocol through non standard ports. I noticed that you can modify port number, but no one is accepted, except for 80 and 443, that are standard ports.

    I tried also to modify pcnsconfig.ini, but I got this error:

    "The ini contains an invalid value for port in section NetworkManagementCard. Using 443 instead".

    It is really not possible to set a non standard port for http/https?

    Thanks
    Fabio

  • wpasquil
    Bill
    =S= Representative
      This discussion is marked as answered
    Bill 8/1/2018 12:44 PM (in response to Fabio)

    Hi,

    The supported port are listed in Schneider Electric FAQ FA159753 "HTTP and HTTPS Allowed Port Values for PowerChute Network Shutdown" 

    Issue:
    HTTP and HTTPS Allowed Port Values for PowerChute Network Shutdown

    Product Line:
    PowerChute Network Shutdown

    Environment:
    All supported OS

    Cause:
    Informational

    Solution:
    The allowed values are: 
    80 or 3052 (when HTTP is selected) 
    443 or 6547 (when HTTPS is selected) 
    5000 - 32768 (when either HTTP or HTTPS is selected)
    Test I changed the web setting of AP9631 for http to port 5000 and rebooted the NMC. I then change the pcnsconfig.ini to log into the NMC via http using port 5000 and restart the PCNS service. When selecting launch from within the PCNS web interface the web interface is launched and I can log in. 
    [NetworkManagementCard]
    mode = single
    IP_1 = 10.218.70.92
    port = 5000
    protocol = http
    enrolWithNMC = true
    acceptCerts = false
    IP_1_Outlet = 1
  • flaserra
    Fabio
    Novice Novice
    Fabio 8/1/2018 1:01 PM (in response to Bill)

    thank you!