    Hey Folks

    I'm hoping this is the right place to ask, I'm looking for a PDU for my home-lab, I've been offered an APC AP7723 for a reasonable price, the fact it can have 2 inputs is even better.

    But does anybody know if it has monitoring and switching for each outlet?

    I'd like to be able to turn on/off each of the devices remotely, at present I have a long trip into the garage! (After doing that 10 times.. it soon gets old).

    Thanks

  • Brad_C
    This discussion is marked as answered

    That isn't a PDU, it's an ATS.

    No, that won't do what you want.

    I have a set up much like you seem to be after. I have an SUA3000 UPS into an AP7721 ATS which then drives an AP7952 PDU.

    The PDU allows me to individually control each outlet, so I can remote power-cycle and do load-shedding when on UPS. The ATS allows me to take the UPS out of circuit for maintenance or have it automatically bypass the UPS if it develops a fault.

     