Loading ...

APC7723 Enabling ssh will cause ATS to reboot? | Racks, Rack Accessories, & Cooling

Home » Spaces » Racks, Rack Accessories, & Cooling » discussion » General » APC7723 Enabling ssh will cause ATS to reboot?

APC7723 Enabling ssh will cause ATS to reboot?

Discussion in Racks, Rack Accessories, & Cooling started by Liam , 7/26/2019 2:23 PM
Login to follow, share, and participate in this space.
Not a member?Join now
Posted in: General

APC7723 Enabling ssh will cause ATS to reboot?

Subscribe to RSS
  • LiamMc

    Hi,

    I've been asked to enable https on some APC7723 units, they are all in production and on critical systems. I read in the manual that "When you enable SSL, you must reboot the Automatic Transfer Switch".

    Does this restart apply to the network management card only, or will the ATS will drop power? D:

    In other parts of the user guide the Network Management Card is usually specifically referenced, not the ATS itself.
    Any clarification would be greatly appreciated.

  • wpasquil
    This discussion is marked as answered

    Hi,

    When you add HTTPS to the network interface of the AP7723 you reboot the network interface only. the ATS remains on line. 

  • LiamMc

    Thanks Bill

Page 1 of 1 (3 items)
Choose your language:  
powered by Communifire
Version 6.0.7207.29305