Can acrd500 rack cooling provide power consumption via SNMP

Subscribe to RSS
  • timlegge

    Hi

    I am attempting to get a accurate data possible on power ussage in my data center.  Is it possible to obtain power consumption form an acrd500 via snmp?

    Tim

  • L2SupportServices-Cooling

    Hello Timothy.

    There is no value for the overall power draw on the cooling units. There is a value for the compressor drive. The compressor is the main power draw on these units with the fans and condensate pump the other motors in the system. The condensate pump is RATED 240V, 4 AMP, 1/10HP. The fan motor is a Max of 900 watts at 240 for the RD500. They are variable speed fans so the power consumption will vary with the speed of the fans. Hopefully this helps.

    Thank you