noob question on air units

Discussion in Racks, Rack Accessories, & Cooling started by Mark , 12/12/2018 11:20 PM
Login to follow, share, and participate in this space.
Not a member?Join now
  • markm
    Mark
    Novice Novice
    Mark 12/12/2018 11:20 PM

    Bit new to this.

    What is the best practice on connecting cooling units to power.

    I have just recently bought some equipment used, and a little confused on some connections.

    I have (2) ACSC100 in row cooling units, in question.

    Also have a Symmetra LX UPS. Do the air units normally power directly from an electrical panel or from the UPS? thanks.

  • L2SupportServices-Cooling
    L2SupportServices-Cooling
    =S= Representative
      This discussion is marked as answered
    L2SupportServices-Cooling 12/17/2018 1:27 PM (in response to Mark)

    Hello. Air cooled units like the ACSC100 are usually connected to utility power (electrical panel) NOT a UPS. This is because the compressor will pull a lot of amps when it starts up and will overload a ups.

    Thank you