  • Emmanuelle

    Hi All,

    I would like your support on how to confirm the PDU uptime for the below models:

    AP8858, AP8953

    I have logged into the PDU and want to make sure that the Uptime mentioned in the parameters is the actual duration when the power was restored and not the network connection (management uptime).

    Thanks in advance.

  • B-DoubleE

    Hi Emmanuelle,

    The uptime given in the web interface is for the network management card, not power output of the PDU. If the management card restarts (which does not impact the power output of the unit) then the uptime will reset.

  • Emmanuelle

    Thanks Matt, is there any way where i can confirm uptime of the PDU related to power?