Loading ...

Smart-UPS X 1000 - SNMP monitoring - HELP! | Smart-UPS & Symmetra LX / RM

Home » Spaces » Smart-UPS & Symmetra LX / RM » discussion » General » Smart-UPS X 1000 - SNMP monitoring - HELP!

Smart-UPS X 1000 - SNMP monitoring - HELP!

Discussion in Smart-UPS & Symmetra LX / RM started by Ronald , 23 days ago
Login to follow, share, and participate in this space.
Not a member?Join now
Posted in: General

Smart-UPS X 1000 - SNMP monitoring - HELP!

Subscribe to RSS
  • RonaldGr

    Hi there,

    In our environment we are monitoring the devices with PRTG.
    I've tried all options it has for APC devices but I cannot find a sensor for the current error state.
    The Smart-UPS X 1000 states: Critical Alarm Battery Disconnected but in PRTG it shows me all is fine.
    Does anybody know which OID I should be using to capture this error?PRTG APC sensors

    web interface X1000

  • RonaldGr

    Hi there,
    I have found a work around for my issue.

    By using the OID 1.3.6.1.4.1.318.1.1.1.2.3.4.0 and setting upper & lower limits I can check the voltage and verify the battery connectivity.

    #closed

  • B-DoubleE

    Hi Ronald,

    To give you an additional data point - the OID .1.3.6.1.4.1.318.1.1.1.11.1.1.0 (upsBasicStateOutputState) has a bunch of flags that can be triggered based on different UPS events. Flag 33 for "no batteries attached" should be flipped to "1" when a battery disconnect event occurs.

Page 1 of 1 (3 items)
Choose your language:  
powered by Communifire
Version 6.0.7207.29305