UPS: Bypass not in range ; high voltage

Discussion in Smart-UPS & Symmetra LX / RM started by Michael , 7/19/2019 8:13 PM
Login to follow, share, and participate in this space.
Not a member?Join now
Posted in: General

UPS: Bypass not in range ; high voltage

Subscribe to RSS
  • MPFlatley

    Hello all, this is my first Post so go easy if I come off as not all knowing :)

    The system is an APC smart-ups RT 10000 with two external battery banks

     

    I am getting alerts for the below error

    Serial Number : 5A1622T25659
    Device Serial Number : AS1623170285
    Date : 07/19/2019
    Time : 11:02:58
    Code : 0x020F

    Critical - UPS: Bypass not in range ; high voltage.

    I have read through some other posts on here similar to my error and they say its a input/output voltage not being the same. Would this be my case too? I am attaching as much as i can for those to review. 

     

    Thanks for your time and help

    Mike

  • liamg

    Hi Mike - 

    Your input and output are both set to 208 and it looks like you have your bypass range set as wide as possible. 

    Everything looks good on the configuration end - I think you're just having some wild swings in input voltage on occasion and the UPS is doing exactly what it's supposed to do. If you're concerned, you could try contacting an electrician or your utility, but you may find that it just clears up on its own.

     

    Thanks

    Liam

Page 1 of 1 (2 items)