Smart-UPS 2200 battery problem

Discussion in Smart-UPS & Symmetra LX / RM started by Bartolo , 5/27/2019 11:36 AM
Login to follow, share, and participate in this space.
Not a member?Join now
Posted in: General

Smart-UPS 2200 battery problem

Subscribe to RSS
  • Bartolo

    The last two times when the UPS runs a self-test there has been an error afterwards.

    Notifications go like this:

    • 0 seconds: self-test started
    • 10 seconds: self-test passed
    • + few more seconds: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately.
    • + few more seconds: A discharged battery condition no longer exists.

    Does this mean that the self-test is wrong and the battery is starting to wear out?

  • liamg

    Hi Bartolo - 

    Either you have a very large load connected to the UPS, you have your low battery signal set very high (default is 2 minutes) or the battery is starting to wear out. When was the battery last replaced? 

    Liam

  • Bartolo

    The battery is less than two years old. I created a support case and they will replace the battery under warranty.