    I have the above UPS where the batteries have completely drained; the terminal reads 6V. Can this value prevent the UPS from starting as this one does when plugged into AC outlet?

  • MattK

    Hi mntambo

    Yes, the SURT UPS range require a certain battery voltage to start up.

    The more recent SRT range is able to start up without battery.

    Regards

    Matt

  • mburi

    Thanks Matt I have resolved the problem after replacing batteries. 