Home » Spaces » Smart-UPS & Symmetra LX / RM » discussion » General » Question about sua48xlbp

Question about sua48xlbp

Discussion in Smart-UPS & Symmetra LX / RM started by Shehab , 11 days ago
Login to follow, share, and participate in this space.
Not a member?Join now
  • Almajhool
    Shehab
    Novice Novice
    Shehab 11 days ago

    hi everyone

    I want to know about configuring the external pack of sua48xlbp in sua3000xli

    is one sua48xlbp = 1 or 2 ex battery pack in the configuration

    also how many sua48xlbp can i connect to the sua3000xli

    I read alot about it but i got confuse because There are alot of products 

    thank in advance

  • ptrk
    Patrik
    Novice Novice
    Patrik 11 days ago (in response to Shehab)

    Yes, this can be quite confusing...  ;)

    1 sua48xlbp = 1 ex battery pack. (1 sua48xlbp contains 2 RBC140 and one RBC140 is made of 2 battery cartridges, so the xlbp-chassi have room for 4 cartridges and they always have to be installed in pairs)

    You can connect up to 10 sua48xlbp to one sua3000xli.

  • Almajhool
    Shehab
    Novice Novice
    Shehab 10 days ago (in response to Patrik)

    Thanks alot