Question about sua48xlbp

Subscribe to RSS
  • Almajhool

    hi everyone

    I want to know about configuring the external pack of sua48xlbp in sua3000xli

    is one sua48xlbp = 1 or 2 ex battery pack in the configuration

    also how many sua48xlbp can i connect to the sua3000xli

    I read alot about it but i got confuse because There are alot of products 

    thank in advance

  • ptrk
    This discussion is marked as answered

    Yes, this can be quite confusing...  ;)

    1 sua48xlbp = 1 ex battery pack. (1 sua48xlbp contains 2 RBC140 and one RBC140 is made of 2 battery cartridges, so the xlbp-chassi have room for 4 cartridges and they always have to be installed in pairs)

    You can connect up to 10 sua48xlbp to one sua3000xli.

  • Almajhool

    Thanks alot