help APC SURT2000XLI fault 10000

Discussion in Smart-UPS & Symmetra LX / RM started by minh , 3/12/2019 10:38 AM
Login to follow, share, and participate in this space.
Not a member?Join now
Posted in: General

help APC SURT2000XLI fault 10000

Subscribe to RSS
  • f14tomcat

    this ups working great in 6 or 7 years then i replaced by surtd5000xli for more power  and after my bigger UPS Surtd5000 sendt to repair ( I have a topic before) I take this old surt2000xli to use  but when I power on (cold start ) with good battery . this ups appear fault led and battery led look like
    1
    0
    0
    0
    0

    my old surt2000xli date I think is 2001 or 2002
    so what happens with my surt2000xli ? :(

  • s.v.s

    Hi Minh,

    If the 1 represents the top LED in the battery bar graph then the 10000 bar graph and fault X LED combination indicates an over temperature event. If the batteries in the SURT2000XLI are from 2001/2002 then chances are these may be causing the event due to old / defective batteries. On the other hand this may also indicate a hardware issue for example with the UPS temperature probe. The easiest way to test if the UPS electronics are not affected is to cross test the system with a known good RBC31.

  • f14tomcat

    Hi Szabi,

    after remove battery to check voltage ~53v  i think it is okay . im reinstall and push test button to power on . every thing working like normal :o
    Thank you for your support!