SRT 8KVA battery says error 0040

Discussion in Smart-UPS & Symmetra LX / RM started by terrence , 2/22/2019 7:24 PM
Login to follow, share, and participate in this space.
Not a member?Join now
Posted in: General

SRT 8KVA battery says error 0040

Subscribe to RSS
  • terrence

    Can anyone state what does this code mean?

    Also is there is a document available that states what all the fault codes mean?

  • terrence

    does anyone know what the code means?

  • MattK
    This discussion is marked as answered

    Hi Terence

    The error message may have been displayed because of weak batteries.  If you have a meter you could measure the terminals of the RBC you should get somewhere in the region of 218v on a good battery.

    Regards

    Matt