Smart-UPS RT 3000 XL turns ouput power off

Discussion in Smart-UPS & Symmetra LX / RM started by Thomas , 7 days ago
Login to follow, share, and participate in this space.
Not a member?Join now
  • quinot
    Thomas
    New Member New Member
    Thomas 7 days ago

    Hello,

    I'd like to understand the incident captured below. The UPS appears to have turned its own output power off but I can't identify why.

    The battery was known to be defective, but this had been the case for several weeks; and there was no event logged regarding input power. I don't understand why the UPS did not continue providing power, since in spite of the faulty battery (which has since then been replaced), there was no recorded loss of input power.

    Complete event log attached. NMC is running version 6.2.1.

     2019-01-01 12:39:54 Device UPS: The battery is now installed.

     2019-01-01

    12:31:25 Device UPS: The output power is turned off.
     2019-01-01 12:31:25 Device UPS: The graceful shutdown period has ended.
     2019-01-01 12:31:25 Device UPS: The battery is not installed properly.
     2019-01-01 12:31:25 Device UPS: Restored the local network management interface-to-UPS communication.
     2019-01-01 12:31:10 System Network service started. IPv6 address FE80::2C0:B7FF:FE58:60B0 assigned by link-local autoconfiguration.
     2019-01-01 12:30:52 System Network Interface coldstarted.
     2019-01-01 12:25:05 Device UPS: The battery is now installed.
     2019-01-01 12:24:45 Device UPS: The battery is not installed properly.
     2019-01-01 11:49:13 Device UPS: The battery is now installed.
     2019-01-01 11:48:52 Device UPS: The battery is not installed properly.
     2019-01-01 10:19:42 Device UPS: The battery is now installed.

    Attachments
  • liamg
    Liam
    =S= Representative
    Liam 4 days ago (in response to Thomas)

    Hi Thomas - 

    It's likely that there was a very brief power event that the unit did not log. The Install/Uninstall alerts are being logged so quickly that the Network card likely couldn't keep up with everything the UPS was reporting. When you start seeing a unit constantly logging installed/uninstalled issues like this it is also possible that the batteries are overheating and causing erratic behavior. I would recommend replacing batteries as soon as you get a bad battery alert, and to disconnect them if you see this type of rapid fire installed/uninstalled errors.

    If your UPS is in warranty you can contact your local tech support team for a replacement.

    Thanks

    Liam