Smart UPS: SRT10KXLI Power Sys Error - 00004

Discussion in Smart-UPS & Symmetra LX / RM started by Mohamed , 1/31/2017 7:04 AM
Login to follow, share, and participate in this space.
Not a member?Join now
Posted in: General

Smart UPS: SRT10KXLI Power Sys Error - 00004

Subscribe to RSS
  • eng.shebl

    Hi

    I have a problem with our UPS as it is notifying me that there is an internal hardware fault and the UPS switched to bypass mode.

    On UPS screen, a message " Power Sys Error - 00004 Contact Customer Service".

    This UPS in the warranty period. 

    How can I solve this problem? 

    Attached event file - data file - debug file

    Attachments
  • GoNz0
    This discussion is marked as answered

    Contacting customer support springs to mind.

  • eng.shebl

    I have contacted the customer support.

    I'm searching if I can do something else to solve this issue.

  • mohamedsayed

    Hi Mohamed,

    how you did solve your issue as i have here the exact problem as yours??

    many thanks if you can help me out

  • hmdstar1
    i have same problem and don`t know how to solve it
  • liamg

    Hi Hamid - 

    if you look at the Event Log on your unit's LCD screen, there should also be an Event Code (typically a 3 digit number). Can you tell me what it is?

    Liam

  • hmdstar1
    This discussion is marked as answered

    Hi dear Liam

    please find the attached photo of smart UPS SRT10KXLI POWER SYS ERROR 00004 

    Thanks 

    Hameed

  • liamg

    Hi Hamid -

    You can try using the "brain dead" procedure to reset this fault:

    • Turn off UPS
    • Disconnect input power
    • Disconnect all batteries (internal and external)
    • Reconnect batteries, reconnect input power, and turn UPS back on

    If this fails to clear the fault, or if the fault returns, you should contact your local tech support team for further assistance or warranty replacement.

    Thanks,

    Liam

  • hmdstar1

    1- SRT10KXLI problem, it showing on screen (Internal RBC needs Replacement on Battery).

    2- SRT6KXLI problem, During normal working day the smoke came from the power supply when we off the UPS after a few hours when we reconnect to the power the UPS cut the Main power feus.

  • liamg

    Hi Hamid - 

    I would suggest contacting your local tech support team to troubleshoot these units and possibly set up a warranty exchange if they are under warranty. You can find your local contact information at https://www.apc.com/support/ 