Loading ...

APC ES700 - Controlled by master not work anymore | Back-UPS & Surge Protectors

Home » Spaces » Back-UPS & Surge Protectors » discussion » General » APC ES700 - Controlled by master not work anymore

APC ES700 - Controlled by master not work anymore

Discussion in Back-UPS & Surge Protectors started by Daniel , 15 days ago
Login to follow, share, and participate in this space.
Not a member?Join now
Posted in: General

APC ES700 - Controlled by master not work anymore

Subscribe to RSS
  • Hello,

    I have had exactly this UPS for 6 years, the APC ES700, and now none of the three "controlled by master" outlets are working.

    I have deactivated the function "master" and the light is off but nothing happens.

    I even removed the battery to do a reset but it's the same.

    No one is talking about this problem in the forums.

    Thank you
    Daniel.

  • On 4/22/2021 9:34 AM, Daniel said:

    Hello,

    I have had exactly this UPS for 6 years, the APC ES700, and now none of the three "controlled by master" outlets are working Prepaid Gift Balance.

    I have deactivated the function "master" and the light is off but nothing happens.

    I even removed the battery to do a reset but it's the same.

    No one is talking about this problem in the forums.

    Thank you
    Daniel.

    It sounds like the unit is going into overload when transferring to battery based on the description. What is does PowerChute report the load is with all equipment connected?  

Page 1 of 1 (2 items)
Choose your language:  
powered by Communifire
Version 8.0.7757.16597