hi , I have large number of PDUs and I want to monitor all of them in on session. ( I cant monitor and manage 30 PDUs by separate ) help me.
StruXureware Data Center Expert(formally Central) 7.x also lets you configure multiple devices at the same time - given they are the same model. I've heard of other people using Solar Winds but have not used it myself.
i'd suggest looking into an SNMP monitoring solution, such as our own StruxureWare Data Center Expert-> http://www.apc.com/products/family/index.cfm?id=350 if that is not what you need, i would look at a free SNMP NMS to do this as I believe it'd be easiest (such as Nagios). All of the PDUs support SNMPv1, v2c, and v3.
I agree. SNMP solutions work great. SolarWinds APM will do this. If not ISX Central. Thanks, Aberrant Technology Group Server Room Design & Construction www.aberrantgroup.com Message was edited by: aberrantgroup
DC Expert is the solution to go for. It can send out alarms or forward snmp traps to your service management software (to open incidents autmatically).
The 7.2 version also has a very neat web interface where you can install wigdgets which give you an immediate overview over alarms, loads etc.
how can I monitor probe temperature of PDUs and what services i can monitor for PDU device?