Loading ...

| Server Room & Data Center Design Best Practices

Home » Spaces » Server Room & Data Center Design Best Practices » discussion » General » How to account for rudundant PSU's

How to account for rudundant PSU's

Discussion in Server Room & Data Center Design Best Practices started by Jacob , 9/23/2011 3:04 PM
Login to follow, share, and participate in this space.
Not a member?Join now
Posted in: General

How to account for rudundant PSU's

Subscribe to RSS
  • When planning a new UPS system, what is the proper way to account for redundant PSUs when planning UPS capacity? For example, if I have a server that has (2) 500W redundant PSUs should the UPS be scaled to handle 1000W or just 500W. I realize this isn't best practice for full redundancy and that the example is probably over simplified, but I am just trying to get an understanding of how I should account for that in my UPS design. Thank you.

  • Hi Skapykat,

    You should size your UPS based on the total load. On most servers, the hardware should distribute the load evenly between the 2 PSU's although some newer lines allow you to specifically configure these loadings.

    I hope this helps,

    Paul.

Page 1 of 1 (2 items)
Choose your language:  
powered by Communifire
Version 8.0.7757.16597