COOLING A HIGH DENSITY DATA CENTER

Subscribe to RSS
  • loropeza

    I am making a basic design for a high density data center, this room has 75 High Density Racks total. I am assuming a power comsumption of 10KW for each Rack and a requirement of 1388 CFM for each unit
    the requirement comes from:
    by APC white paper: 18kw ---->2500 CFM
    so 10kw--->1388 CFM
    75 units in the room x 1388=104100 CFM
    so my flow requirement is more or less 104100 CFM for this computer room
    I saw that I can configure a system based with 2 chillers of your brand, part number ACCH220N-ABA-D10S which is a Unit capable of a flow 49600 CFM. with two units I can cover my requirements.

    so for this system I have two questions:
    question 1: do I have anything wrong in my assumptions or numbers?

    question 2:
    I am trying to avoid Chillers because I dont want to put anything on the roof. what other alternatives do I have?

  • KVAr

    If the climate isn't cool enough you can't avoid chillers. Even if it's just a few weeks out of the year, that's a few weeks out of the year you'll have to take servers out of service for