Planning data center

Discussion in Server Room & Data Center Design Best Practices started by Chelsea , 1/13/2010 10:33 AM
Login to follow, share, and participate in this space.
Not a member?Join now
Posted in: General

Planning data center

Subscribe to RSS
  • mfitzsimmons

    Whether or not this is a good design depends a lot on the intended use.
    This a good design for a very low density application, say less than 1 kW per rack and no more than 2 kW in any rack.
    If the expected use is modern high density servers then this design will not support the load.

    A lot more data would be required to be able to give a valid critique.

  • lilama45-1

    Hello everybody,
    I have arranged a data center plan, please give your opions about this plan, is it right or wrong? Thank you very much.