AP7580 PDU Extender

Discussion in Server Room & Data Center Design Best Practices started by Paul , 1/17/2009 6:09 AM
Login to follow, share, and participate in this space.
Not a member?Join now
Posted in: General

AP7580 PDU Extender

Subscribe to RSS
  • enigma62333

    Pardon my naivety but we at my organization are contracting for cage space in a data center and they are supplying 208/30 to the Cage, We already own some metered AP7830 PDU's that take 120/20 input. Would it, if we were to purchase one of these, be able to step-down the voltage from 208 to 120 for the 7830's? I have read the documentation but it was not clear to me.

    Thanks in advance for the assistance.

  • ipicKedawinna

    the PDU extender doesnt "step down" the voltage, it just splits the hot legs that you have already. it uses a L14-30 plug on it which is 120/240v.

    i dont see why you couldnt do this if you have an L14-30 receptable available..

Page 1 of 1 (2 items)