While cleaning wires out of a rack I was decommissioning I found an old AP9512TBLK temperature probe with the PS/2 style connector. There was no 9320 to go with it, and for as long as I've been here we've used 9631 cards in the UPS for environmental monitoring. I'm interested in using it for a pet project that needs a temperature sensor and was wondering if anyone could help me with the pinout of the connector, and anything else I might need to know to use it.
Thanks!
Necropost, though. Take connector flat side down, pins face . Counting from right-bottom as 1:
Note: there LM358N inside. It take either single polar voltage, or dual polar. Working voltage is 3-32V (single polarity), +-1,5 - +-16V. I don't check signal polarity/range.