Loading ...

| Other Environmental Monitoring Products & Questions

ups failure to see mains

Discussion in Other Environmental Monitoring Products & Questions started by Katongo , 9/25/2016 7:10 PM
Login to follow, share, and participate in this space.
Not a member?Join now
Posted in: General

ups failure to see mains

Subscribe to RSS
  • katongo

    Dear friends,

    I HAVE 2 BY SUVTP 40KH WHICH ARE EXPERIENCING NO MAINS ERROR. MAINS NOT AVAILABLE IS THE MAIN ERROR EVEN WHEN I CAN CONFIRM THE MAINS AVAILABILITY. THE OTHER ALARM IS BATTERY DISCHARGED. HOW CAN I BE HELPED.

    katongo
  • Haseeb
    This discussion is marked as answered

    Hello 

    Referencing the SUVT Operations Manual, please refer to page 42.

    http://www.apcmedia.com/salestools/AHIE-83NAUF/AHIE-83NAUF_R0_EN.pdf?sdirect=true

    Mains Not Available. Input Freq/Volt Out of Range.

    Meaning: The frequency or voltage is out of acceptable range for normal operation.
    Corrective Action: Correct the input voltage to provide acceptable voltage or frequency.

    Battery Discharged.

    Meaning: The UPS is in battery operation and the battery charge is low. Note: Runtime is limited in duration.
    Corrective Action: No corrective action is necessary. Shut down the system and the load equipment or restore incoming voltage.

    Kind Regards

    Haseeb

Page 1 of 1 (2 items)
Choose your language:  
powered by Communifire
Version 7.0.7496.13049