Loading ...
Home » Spaces » Data Center & Facility 3 Phase UPS » discussion » General » APC Symmetra 40k Power Module, Battery Module, Intelligence Module.

APC Symmetra 40k Power Module, Battery Module, Intelligence Module.

Discussion in Data Center & Facility 3 Phase UPS started by Fazail , 7/24/2017 7:56 AM
Login to follow, share, and participate in this space.
Not a member?Join now
  • fazail
    Fazail
    Novice Novice
    Fazail 7/24/2017 7:56 AM APC Symmetra 40k Power Module, Battery Module, Intelligence Module.
    Attachments
  • wpasquil
    Bill
    =S= Representative
    Bill 7/24/2017 2:44 PM (in response to Fazail)

    Hi,

    Whenever any module or card is to be reseated or replaced the UPS should be placed into Maintenance Bypass before proceeding. This will eliminate any possibility of system downtime. This procedure applies to: Intelligence Modules, Power Modules, Static Switch Modules, Battery Monitor Boards, Power Supplies, XR Communication Cards and External Switch Gear Cards.

    Please follow the Installation and Operation Guide for instructions on how to place a Symmetra PX into bypass. And you should verify compatibility of any replacement modules with local support before proceeding. 

  • Page 1 of 1 (2 items)
Choose your language:  
powered by Communifire
Version 5.2.6420.11692