    Hi Guys,

    Please I have 2 units of SUVT and 2 units of Galaxy 3500. Each Galaxy 3500 will support seperate load and one of the SUVT will support another load and the other SUVT will be a redundant in case any of the remaining UPS fails. Please i need a response to know if I can parallel all the UPS


  • clarkson
    =S= Representative
    Rob 11/24/2010 9:43 PM (in response to Olufemi)

    The three phase support team here says it is possible but you will need a parallel bypass panel. It would be best to APC support in your region; A rep should be able to get it approved with a configuration team and get you the details.

  • mittons
    New Member
    New Member
    tim 2/16/2011 8:35 PM (in response to Rob)

    would he also need the separate CAN I/O boards for each unit ?

    also confirming that the power modules are the parallel version ? ending with -p suffix..