ups failure

Discussion in Data Center & Facility 3 Phase UPS started by Katongo , 12/19/2016 12:53 PM
Login  to follow, share, and participate in this space.
Not a member?Join now
  • katongo
    Katongo
    Novice
    Novice
    Katongo 12/19/2016 12:53 PM

    How can i resolve the problem below?
    I have a 30kva UPS with serial number PS0913140294 and module serial number PS0913240570. This unit machine has a system failure detected by surveillance alarm. on normal start-up, this error is always there but it doesn't come immediately when i cold-start the unit. when i start the unit without utility power, it fails to turn on the load. when i give it utility power whilst on battery, it says no alarms present but the load would still be off. when i command it to turn load on, i hear the contactor energising and before then load is on the contactor de-energises again within a second, then the alarm "system failure detected by surveillance "appears.
    on raw status data, this is what i got: m state=020302 00000000 00000000 00000001.
    May you please help me determine what is wrong with this unit.

    katongo
  • wpasquil
    Bill
    =S= Representative
    Bill 12/19/2016 1:32 PM (in response to Katongo)

    Hi,

    What is the model UPS?

  • Page 1 of 1 (2 items)