Discussion in Data Center & Facility 3 Phase UPS started by Luis Fernando , 5/10/2016 10:42 PM
Login to follow, share, and participate in this space.
Not a member?Join now
  • LFRuiz
    Luis Fernando
    Novice Novice
    Luis Fernando 5/10/2016 10:42 PM

    Hi, I want to know if a SY200K250D can be expanded to a 250kVA/KW configuration and what modules would I have to add?

    Or do I have to change frames and go with the SY250K500D?

    Thanks.

  • dcops
    Daniel
    Novice Novice
    Daniel 5/11/2016 12:08 AM (in response to Luis Fernando)

    So long as your site wiring was for the 250kw load,  it should have two empty slots for 25KW modules.  

  • AliRaza
    Ali
    New Member New Member
    Ali 5/11/2016 6:42 AM (in response to Luis Fernando)

    Yes i can be expanded upto 250kVA/KW . But if your load will be between ( 225-250KVA/KW) then it will not be internal redundant. 

    You simply need to add SYPM25KD Qty 02/- 

    Here is link for more information

    http://www.apc.com/shop/pk/en/products/APC-Symmetra-PX-25kW-Power-Module-400-480V/P-SYPM25KD

  • LFRuiz
    Luis Fernando
    Novice Novice
    Luis Fernando 5/11/2016 4:09 PM (in response to Ali)

    Thanks for your reply.

    Do I need to add any battery modules?

    Thanks.

  • ptrk
    Patrik
    Novice Novice
    Patrik 12/9/2016 3:44 PM (in response to Luis Fernando)

    You should have at least 1.6 batterymodules (1 module = 1 row = 6 units) per powermodule.

    So, 10 powermodules require minimum 10 x 1.6 = 16 modules = 2 full battery frames.