    Hus 14 days ago

    Hi team, 

    We have small datacenter with sensitive and high secure data and servers. Currently it is one row with 7 racks. Soon we will add another servers racks. The cooling system is HVAC which damaged some servers. I am willing to install in row cooling system from your products but I have some questions that I need your answers to provide our project management team to start purchasing and so on.

    My questions are:

    1- are your in row cooling products enough to cool the DC, so I can stop HVAC?

    2-for redundancy, shall I get two units. Each row has one cooling unit?

    3-do you have built in monitoring system, so I can monitor environment and getting alarms, also system for redundancy ?

    4-what is the best unit which fits with our requirements, also it doesn't need complex installation (plug and play)?

    5-Could you please provide me some links for the proposed products by you? 

    Regards

  • L2SupportServices-Cooling
    L2SupportServices-Cooling
    =S= Representative
    L2SupportServices-Cooling 13 days ago (in response to Hus)

    Hello Hus. Here are some recommendations for your questions.

    1- are your in row cooling products enough to cool the DC, so I can stop HVAC?

    A- This depends on the heat load in your room. We have a variety of different sized Inrow cooling units that can cool between 5kw-70KW of heat load per cooling unit.

    2-for redundancy, shall I get two units. Each row has one cooling unit?

    A-Most of our DX (air cooled) Inrow units can do lead/lag to allow a backup unit for redundancy. This will also depend on the setup of the room to determine how many units would be needed to have redundancy in the room.

    3-do you have built in monitoring system, so I can monitor environment and getting alarms, also system for redundancy ?

    A- All of our Inrow units come with a network card in them that allows network access to them for monitoring and alarm emails. They will just need to be hooked up to your network.

    4-what is the best unit which fits with our requirements, also it doesn't need complex installation (plug and play)?

    A-This will depend on your requirements for the Data center. Please see below for suggestion on getting help on sizing.

    5-Could you please provide me some links for the proposed products by you?

    A- Here is a link to our website for our cooling products.

    http://www.apc.com/shop/us/en/categories/cooling/N-yp2yk2

    I recommend calling into your local sales support as they can can walk you through the selection process to see which of the Inrow options will work best for your data center. The number can be found on our website under support tab and contact us. 

    Thank you