home » spaces » Racks, Rack Accessories, & Cooling » discussion » General » OID clarification for controlling outlets via SNMP on guest/linked rPDU's?

OID clarification for controlling outlets via SNMP on guest/linked rPDU's?

Discussion in Racks, Rack Accessories, & Cooling started by Brian , 20 days ago
Login  to follow, share, and participate in this space.
Not a member?Join now
  • scrupul0us
    Brian
    Novice
    Novice
    Brian 20 days ago

    I am looking to clarify my understanding of the OID(s) used for controlling outlets on linked/guest rPDUs.

    We all know the base OID for controlling a single rPDU:

    rPDUOutletControlIndex 1.3.6.1.4.1.318.1.1.12.3.3.1.1.1
    rPDUOutletControlOutletName rPDUOutletControlOutletName 1.3.6.1.4.1.318.1.1.12.3.3.1.1.2
    rPDUOutletControlOutletPhase rPDUOutletControlOutletPhase 1.3.6.1.4.1.318.1.1.12.3.3.1.1.3
    rPDUOutletControlOutletCommand rPDUOutletControlOutletCommand 1.3.6.1.4.1.318.1.1.12.3.3.1.1.4
    rPDUOutletControlOutletBank rPDUOutletControlOutletBank 1.3.6.1.4.1.318.1.1.12.3.3.1.1.5

    I have found what I think is the correct OID path for controlling outlets in rPDU2 at: enterprises.318.1.1.26.9.2.4 however I wasn't able to find anything concrete to shore up my assumption:

    rPDU2OutletSwitchedControlTable rPDU2OutletSwitchedControlTable 1.3.6.1.4.1.318.1.1.26.9.2.4
    rPDU2OutletSwitchedControlEntry rPDU2OutletSwitchedControlEntry 1.3.6.1.4.1.318.1.1.26.9.2.4.1
    rPDU2OutletSwitchedControlIndex rPDU2OutletSwitchedControlIndex 1.3.6.1.4.1.318.1.1.26.9.2.4.1.1
    rPDU2OutletSwitchedControlModule rPDU2OutletSwitchedControlModule 1.3.6.1.4.1.318.1.1.26.9.2.4.1.2
    rPDU2OutletSwitchedControlName rPDU2OutletSwitchedControlName 1.3.6.1.4.1.318.1.1.26.9.2.4.1.3
    rPDU2OutletSwitchedControlNumber rPDU2OutletSwitchedControlNumber 1.3.6.1.4.1.318.1.1.26.9.2.4.1.4
    rPDU2OutletSwitchedControlCommand rPDU2OutletSwitchedControlCommand 1.3.6.1.4.1.318.1.1.26.9.2.4.1.5

    When I walk that it appears to be what I want but before I made assumptions I wanted to ask.

    I've attached a txt file with the output from snmpwalk on 1.3.6.1.4.1.318.1.1.26.9.2.4 if that helps.

    Thank you =)

    Attachments
  • ipicKedawinna
    Angela
    =S= Representative
    Angela 20 days ago (in response to Brian)

    Hi Brian,

    Any OID that begins with rPDU is intended to be used with our older style PDUs with model numbers in the AP7XXX range - AP79XX specifically for switched outlet models.

    Any OID that begins with rPDU2 is intended to be used with or 2G or 2nd generation PDUs that have model numbers beginning with AP8XXX. The switched models are AP89XX and AP86XX.

    If you are using the AP8XXX series and are using the Network Port Sharing feature - which means you'd have host and guest PDUs, then I suggest to read here and refer to the SNMP section to understand how SNMP changes when you have more than one PDU at a single IP address -> http://www.apc.com/us/en/faqsFA164436 

    Essentially, you'll need to pay attention to the index numbers for each rPDU2 OID and know which PDU is at which SNMP index, especially if you have more than two PDUs where it can be a little complex. And it gets even more complex if you have a mix and match of PDUs that are switched and those that are metered because certain OIDs are only intended for Switched PDUs.

    Anyway, please review what I shared here and let us know if you need any further clarification afterwards.

  • scrupul0us
    Brian
    Novice
    Novice
    Brian 18 days ago (in response to Angela)

    Angela,

    Thanks, I've gone through and ensured outlet# => index => index device owner.

    To simplify (please correct me if I'm wrong), to reboot outlet 24 on a PDU-B in a shared gen2 PDU implementation via SNMP I'd send "3" to:

    enterprises.318.1.1.26.9.2.4.1.5.48

    ...where 48 is the index assigned to port 24 on PDU-B.

    http://oidref.com/1.3.6.1.4.1.318.1.1.26.9.2.4.1.5

    ...seems to confirm this - just crossing my T's and dotting my I's. Thanks =)

  • ipicKedawinna
    Angela
    =S= Representative
    Angela 18 days ago (in response to Brian)

    Hi Brian,

    That looks right. I'd then guess you probably have two, switched 24 outlet PDUs so instance 48 on that OID would indeed be outlet #24 on your second PDU.