Loading ...
home » spaces » Racks, Rack Accessories, & Cooling » discussion » General » APC8941 Firmware upgrade

APC8941 Firmware upgrade

Discussion in Racks, Rack Accessories, & Cooling started by Luca , 2/25/2017 1:49 AM
Login  to follow, share, and participate in this space.
Not a member?Join now
  • Luca72
    Luca
    Novice
    Novice
    Luca 2/25/2017 1:49 AM

    Hello, 

    we are planning to upgrade firmware on several racks PDU. In regards to the model APC8941 documentation indicates bootmon, AOS  and application (rpdu2g) file update is required. We are planning uploading using ftp or scp. What is not clear from the documentation is whether any of those upgrade fill impact normal power supply operation during PDU flash/reload. We are not concerned about PDU's network management, rather power supply to attached devices impact. As we have deployed different PDU models and APC8941 is one among them in production, this can be considered a general upgrade question. 

    Thank you,

    Luca

  • wpasquil
    Bill
    =S= Representative
    Bill 3/1/2017 6:12 PM (in response to Luca)

    Hi,

    You can upgrade the firmware on the network card without taking the load down. The card/s will reboot but power will not be cut to the load.

  • Luca72
    Luca
    Novice
    Novice
    Luca 3/3/2017 9:18 AM (in response to Bill)

    Hi Bill, 

    Just to make sure my understanding is correct, by upgrading the firmware on the network card you mean upgrading all three files, bootmon, AOS and rpdu2g files on the Network Management Card? 

    Thank you,

    Luca

  • voidstar
    voidstar
    Expert
    Expert
    voidstar 3/3/2017 10:56 PM (in response to Luca)

    Only AOS and RPDU2G files are absolutely required, but you can upgrade bootmon also.

  • Luca72
    Luca
    Novice
    Novice
    Luca 3/6/2017 3:48 AM (in response to voidstar)

    I am under the assumption nor bootmon, AOS and RPDU2G upgrade are impacting outlet's power supply capabilities. In other words none of those upgrades will stop normal power supply operations during the firmware upgrade. Is it my assumption correct?   

    Previous reply from Bill seems to validate my assumption however what I was not sure about is whether "firmware on the network card" are just bootmon, AOS and RPDU2G files. 

  • voidstar
    voidstar
    Expert
    Expert
    voidstar 3/6/2017 4:50 AM (in response to Luca)

    The bootmon, aos, and RPDU app files are all applied to the network management card itself. I read Bill's statement the same way you do. In all the devices I work with (UPSes) device functionality is done by a separate processor.

  • Page 1 of 1 (6 items)
Choose your language:  English  
powered by Communifire
Version 5.0.5741.40378