Unable to lunch PDU via web

Discussion in Racks, Rack Accessories, & Cooling started by eudoro , 24 days ago
Login to follow, share, and participate in this space.
Not a member?Join now
  • esantos17
    eudoro
    New Member New Member
    eudoro 24 days ago

    Dear Forum,

    When i try to attemp the PDU device it appear the error below:

    I can login to PDU via telnet as showed below

    Compared with another device ( PDU) that is ok ( i can login via web) it seem to be the same and Ok.

    Can you please advice me?

    PS: i have some important equipament connected to this PDU.

    I appreciate your help

    Attachments
  • B-DoubleE
    Matt
    =S= Representative
    Matt 24 days ago (in response to eudoro)

    Hello,

    This error can happen when the firmware application does not load properly. It looks like you're a few revisions behind the current release revision of rPDU firmware - I would recommend starting with a firmware upgrade (which can be done while the PDU is in production). You can get the latest rev of FW here: http://www.apc.com/us/en/tools/download/download.cfm?sw_sku=SFRPDU2G644&software_id=MFOI-ADJJT2&family=&part_num=&swfam=55_187&tsk=

  • ipicKedawinna
    Angela
    =S= Representative
    Angela 24 days ago (in response to eudoro)

    You should upgrade all of your units that have 6.0.9 firmware on them as soon as possible, as shown in your screenshot. Please read this information bulletin on why -> http://www.apc.com/us/en/faqs/FA237061 