Loading ...
Home » Spaces » Smart-UPS & Symmetra LX / RM » discussion » General » SRCP001 parallel kit: compatible series

SRCP001 parallel kit: compatible series

Discussion in Smart-UPS & Symmetra LX / RM started by Carlos , 9 days ago
Login to follow, share, and participate in this space.
Not a member?Join now
  • CharlieChannels
    Carlos
    New Member New Member
    Carlos 9 days ago

    Kind greetings! May I use the parallel kit SRCPK001 on two tower SRT6KXLI units? (redundancy purposes). I saw a post mentioning its use on SRC models only...

    If not possible, which would be the right way to connect the redundantly? Thank you for your kind advice!

  • wpasquil
    Bill
    =S= Representative
    Bill 9 days ago (in response to Carlos)

    Hi,

    The kit is not compatible with SRT model Smart-UPS. You can pair SRT Smart-UPS in redundant fashion with PowerChute Network Shutdown. See Application Note 98. 

  • CharlieChannels
    Carlos
    New Member New Member
    Carlos 9 days ago (in response to Bill)

    Thank you for your prompt reply, Bill.... I went through the Application Note 98 and it solely refers to a server backup scenario. What I'm trying to protect is a delicate science lab instrument, where I won't have a Powerchute software controlling the UPSs. What are my options? Choose SRC units instead, in spite of being "budget" alternatives?

  • Page 1 of 1 (3 items)
Choose your language:  
powered by Communifire
Version 5.2.6420.11692