Loading ...
Home » Spaces » Smart-UPS & Symmetra LX / RM » discussion » General » Smart UPS 1500 X Randomly Shuts Down

Smart UPS 1500 X Randomly Shuts Down

Discussion in Smart-UPS & Symmetra LX / RM started by Matt , 17 days ago
Login to follow, share, and participate in this space.
Not a member?Join now
  • Farmhouse1904
    Matt
    Novice Novice
    Matt 17 days ago

    I have a Smart UPS 1500 X (SMX1500RM2UNC) with one external battery pack (SMX48RMBP2U) that just powered down all the outlet groups for no apparent reason.  

    The unit is not that old, it's been in service since December 2016 (manufacture date is October 2016).  The load on it is rather low, 25%-30%.

    Early this morning it appeared to be switching rapidly between shutting down and powering up:
    ----------------
    06/03/2018 09:01:56 Device UPS: The output power is now turned on. 0x0113
    06/03/2018 09:01:56 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned on. 0x0134
    06/03/2018 09:01:56 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned on. 0x0134
    06/03/2018 09:01:56 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned on. 0x0134
    06/03/2018 09:01:50 Device UPS: The output power is turned off. 0x0114
    06/03/2018 09:01:50 Device UPS: The graceful shutdown period has ended. 0x014F
    06/03/2018 09:01:50 Device UPS: Switched outlet group 3, Outlet Group 3, has been commanded to shutdown with on delay. 0x0174
    06/03/2018 09:01:50 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned off. 0x0135
    06/03/2018 09:01:50 Device UPS: Switched outlet group 2, Outlet Group 2, has been commanded to shutdown with on delay. 0x0174
    06/03/2018 09:01:50 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned off. 0x0135
    06/03/2018 09:01:50 Device UPS: Switched outlet group 1, Outlet Group 1, has been commanded to shutdown with on delay. 0x0174
    06/03/2018 09:01:50 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned off. 0x0135
    06/03/2018 07:25:27 Device UPS: The output power is now turned on. 0x0113
    06/03/2018 07:25:27 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned on. 0x0134
    06/03/2018 07:25:27 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned on. 0x0134
    06/03/2018 07:25:27 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned on. 0x0134
    06/03/2018 07:25:21 Device UPS: The output power is turned off. 0x0114
    06/03/2018 07:25:21 Device UPS: The graceful shutdown period has ended. 0x014F
    06/03/2018 07:25:21 Device UPS: Switched outlet group 3, Outlet Group 3, has been commanded to shutdown with on delay. 0x0174
    06/03/2018 07:25:21 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned off. 0x0135
    06/03/2018 07:25:21 Device UPS: Switched outlet group 2, Outlet Group 2, has been commanded to shutdown with on delay. 0x0174
    06/03/2018 07:25:21 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned off. 0x0135
    06/03/2018 07:25:21 Device UPS: Switched outlet group 1, Outlet Group 1, has been commanded to shutdown with on delay. 0x0174
    06/03/2018 07:25:21 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned off. 0x0135
    06/03/2018 07:18:37 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned on. 0x0134
    06/03/2018 07:18:37 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned on. 0x0134
    06/03/2018 07:18:37 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned on. 0x0134
    06/03/2018 07:18:36 Device UPS: The output power is now turned on. 0x0113
    06/03/2018 07:18:32 Device UPS: The output power is turned off. 0x0114
    06/03/2018 07:18:32 Device UPS: The graceful shutdown period has ended. 0x014F
    06/03/2018 07:18:31 Device UPS: Switched outlet group 3, Outlet Group 3, has been commanded to shutdown with on delay. 0x0174
    06/03/2018 07:18:31 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned off. 0x0135
    06/03/2018 07:18:31 Device UPS: Switched outlet group 2, Outlet Group 2, has been commanded to shutdown with on delay. 0x0174
    06/03/2018 07:18:31 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned off. 0x0135
    06/03/2018 07:18:31 Device UPS: Switched outlet group 1, Outlet Group 1, has been commanded to shutdown with on delay. 0x0174
    06/03/2018 07:18:31 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned off. 0x0135
    06/03/2018 07:18:29 Device UPS: The output power is now turned on. 0x0113
    06/03/2018 07:18:29 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned on. 0x0134
    06/03/2018 07:18:29 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned on. 0x0134
    06/03/2018 07:18:29 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned on. 0x0134
    06/03/2018 07:18:24 Device UPS: The output power is turned off. 0x0114
    06/03/2018 07:18:24 Device UPS: The graceful shutdown period has ended. 0x014F
    06/03/2018 07:18:23 Device UPS: Switched outlet group 3, Outlet Group 3, has been commanded to shutdown with on delay. 0x0174
    06/03/2018 07:18:23 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned off. 0x0135
    06/03/2018 07:18:23 Device UPS: Switched outlet group 2, Outlet Group 2, has been commanded to shutdown with on delay. 0x0174
    06/03/2018 07:18:23 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned off. 0x0135
    06/03/2018 07:18:23 Device UPS: Switched outlet group 1, Outlet Group 1, has been commanded to shutdown with on delay. 0x0174
    06/03/2018 07:18:23 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned off. 0x0135
    06/03/2018 07:18:02 Device UPS: The output power is now turned on. 0x0113
    06/03/2018 07:18:01 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned on. 0x0134
    06/03/2018 07:18:01 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned on. 0x0134
    06/03/2018 07:18:01 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned on. 0x0134
    06/03/2018 07:17:56 Device UPS: The output power is turned off. 0x0114
    06/03/2018 07:17:56 Device UPS: The graceful shutdown period has ended. 0x014F
    06/03/2018 07:17:56 Device UPS: Switched outlet group 3, Outlet Group 3, has been commanded to shutdown with on delay. 0x0174
    06/03/2018 07:17:56 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned off. 0x0135
    06/03/2018 07:17:56 Device UPS: Switched outlet group 2, Outlet Group 2, has been commanded to shutdown with on delay. 0x0174
    06/03/2018 07:17:56 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned off. 0x0135
    06/03/2018 07:17:56 Device UPS: Switched outlet group 1, Outlet Group 1, has been commanded to shutdown with on delay. 0x0174
    06/03/2018 07:17:56 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned off. 0x0135
    06/03/2018 07:17:41 Device UPS: Restored the local network management interface-to-UPS communication. 0x0101
    06/03/2018 07:17:28 Device Environment: Restored the local network management interface-to-integrated Environmental Monitor (Universal I/O at Port 1) communication. 0x0344
    06/03/2018 07:17:26 System Network service started. IPv6 address FE80::2C0:B7FF:FEDA:1ECA assigned by link-local autoconfiguration. 0x0007
    06/03/2018 07:17:24 System Network service started. System IP is 10.5.0.15 from manually configured settings. 0x0007
    06/03/2018 07:17:19 System Network Interface restarted. 0x0002
    06/03/2018 07:17:12 Device UPS: The output power is turned off. 0x0114
    06/03/2018 07:17:12 Device UPS: The graceful shutdown period has ended. 0x014F
    06/03/2018 07:17:11 Device UPS: Switched outlet group 3, Outlet Group 3, has been commanded to shutdown with on delay. 0x0174
    06/03/2018 07:17:11 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned off. 0x0135
    06/03/2018 07:17:11 Device UPS: Switched outlet group 2, Outlet Group 2, has been commanded to shutdown with on delay. 0x0174
    06/03/2018 07:17:11 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned off. 0x0135
    06/03/2018 07:17:11 Device UPS: Switched outlet group 1, Outlet Group 1, has been commanded to shutdown with on delay. 0x0174
    06/03/2018 07:17:11 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned off. 0x0135
    06/03/2018 07:17:02 Device UPS: The output power is now turned on. 0x0113
    06/03/2018 07:17:02 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned on. 0x0134
    06/03/2018 07:17:02 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned on. 0x0134
    06/03/2018 07:17:02 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned on. 0x0134
    06/03/2018 07:16:57 Device UPS: The output power is turned off. 0x0114
    06/03/2018 07:16:57 Device UPS: The graceful shutdown period has ended. 0x014F
    06/03/2018 07:16:56 Device UPS: Switched outlet group 3, Outlet Group 3, has been commanded to shutdown with on delay. 0x0174
    06/03/2018 07:16:56 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned off. 0x0135
    06/03/2018 07:16:56 Device UPS: Switched outlet group 2, Outlet Group 2, has been commanded to shutdown with on delay. 0x0174
    06/03/2018 07:16:56 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned off. 0x0135
    06/03/2018 07:16:56 Device UPS: Switched outlet group 1, Outlet Group 1, has been commanded to shutdown with on delay. 0x0174
    06/03/2018 07:16:56 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned off. 0x0135
    06/03/2018 07:15:19 Device UPS: The output power is now turned on. 0x0113
    06/03/2018 07:15:19 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned on. 0x0134
    06/03/2018 07:15:19 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned on. 0x0134
    06/03/2018 07:15:19 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned on. 0x0134
    06/03/2018 07:15:13 Device UPS: The output power is turned off. 0x0114
    06/03/2018 07:15:13 Device UPS: The graceful shutdown period has ended. 0x014F
    06/03/2018 07:15:13 Device UPS: Switched outlet group 3, Outlet Group 3, has been commanded to shutdown with on delay. 0x0174
    06/03/2018 07:15:13 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned off. 0x0135
    06/03/2018 07:15:13 Device UPS: Switched outlet group 2, Outlet Group 2, has been commanded to shutdown with on delay. 0x0174
    06/03/2018 07:15:13 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned off. 0x0135
    06/03/2018 07:15:13 Device UPS: Switched outlet group 1, Outlet Group 1, has been commanded to shutdown with on delay. 0x0174
    06/03/2018 07:15:13 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned off. 0x0135
    06/03/2018 07:15:13 Device UPS: The output power is now turned on. 0x0113
    06/03/2018 07:15:13 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned on. 0x0134
    06/03/2018 07:15:13 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned on. 0x0134
    06/03/2018 07:15:13 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned on. 0x0134
    06/03/2018 07:15:07 Device UPS: The output power is turned off. 0x0114
    06/03/2018 07:15:07 Device UPS: The graceful shutdown period has ended. 0x014F
    06/03/2018 07:15:07 Device UPS: Switched outlet group 3, Outlet Group 3, has been commanded to shutdown with on delay. 0x0174
    06/03/2018 07:15:07 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned off. 0x0135
    06/03/2018 07:15:07 Device UPS: Switched outlet group 2, Outlet Group 2, has been commanded to shutdown with on delay. 0x0174
    06/03/2018 07:15:07 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned off. 0x0135
    06/03/2018 07:15:07 Device UPS: Switched outlet group 1, Outlet Group 1, has been commanded to shutdown with on delay. 0x0174
    06/03/2018 07:15:07 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned off. 0x0135
    06/03/2018 07:15:05 Device UPS: The output power is now turned on. 0x0113
    06/03/2018 07:15:05 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned on. 0x0134
    06/03/2018 07:15:05 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned on. 0x0134
    06/03/2018 07:15:05 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned on. 0x0134
    06/03/2018 07:15:00 Device UPS: The output power is turned off. 0x0114
    06/03/2018 07:15:00 Device UPS: The graceful shutdown period has ended. 0x014F
    06/03/2018 07:14:59 Device UPS: Switched outlet group 3, Outlet Group 3, has been commanded to shutdown with on delay. 0x0174
    06/03/2018 07:14:59 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned off. 0x0135
    06/03/2018 07:14:59 Device UPS: Switched outlet group 2, Outlet Group 2, has been commanded to shutdown with on delay. 0x0174
    06/03/2018 07:14:59 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned off. 0x0135
    06/03/2018 07:14:59 Device UPS: Switched outlet group 1, Outlet Group 1, has been commanded to shutdown with on delay. 0x0174
    06/03/2018 07:14:59 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned off. 0x0135
    06/03/2018 07:14:56 Device UPS: The output power is now turned on. 0x0113
    06/03/2018 07:14:56 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned on. 0x0134
    06/03/2018 07:14:56 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned on. 0x0134
    06/03/2018 07:14:56 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned on. 0x0134
    06/03/2018 07:14:51 Device UPS: The output power is turned off. 0x0114
    06/03/2018 07:14:51 Device UPS: The graceful shutdown period has ended. 0x014F
    06/03/2018 07:14:51 Device UPS: Switched outlet group 3, Outlet Group 3, has been commanded to shutdown with on delay. 0x0174
    06/03/2018 07:14:51 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned off. 0x0135
    06/03/2018 07:14:51 Device UPS: Switched outlet group 2, Outlet Group 2, has been commanded to shutdown with on delay. 0x0174
    06/03/2018 07:14:51 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned off. 0x0135
    06/03/2018 07:14:51 Device UPS: Switched outlet group 1, Outlet Group 1, has been commanded to shutdown with on delay. 0x0174
    06/03/2018 07:14:51 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned off. 0x0135
    06/03/2018 07:13:56 Device UPS: The output power is now turned on. 0x0113
    06/03/2018 07:13:56 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned on. 0x0134
    06/03/2018 07:13:56 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned on. 0x0134
    06/03/2018 07:13:56 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned on. 0x0134
    06/03/2018 07:13:52 Device UPS: The output power is turned off. 0x0114
    06/03/2018 07:13:52 Device UPS: The graceful shutdown period has ended. 0x014F
    06/03/2018 07:13:52 Device UPS: Switched outlet group 3, Outlet Group 3, has been commanded to shutdown with on delay. 0x0174
    06/03/2018 07:13:52 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned off. 0x0135
    06/03/2018 07:13:52 Device UPS: Switched outlet group 2, Outlet Group 2, has been commanded to shutdown with on delay. 0x0174
    06/03/2018 07:13:52 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned off. 0x0135
    06/03/2018 07:13:52 Device UPS: Switched outlet group 1, Outlet Group 1, has been commanded to shutdown with on delay. 0x0174
    06/03/2018 07:13:51 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned off. 0x0135
    06/03/2018 07:13:37 Device UPS: The output power is now turned on. 0x0113
    06/03/2018 07:13:36 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned on. 0x0134
    06/03/2018 07:13:36 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned on. 0x0134
    06/03/2018 07:13:36 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned on. 0x0134
    06/03/2018 07:13:32 Device UPS: The output power is turned off. 0x0114
    06/03/2018 07:13:32 Device UPS: The graceful shutdown period has ended. 0x014F
    06/03/2018 07:13:31 Device UPS: Switched outlet group 3, Outlet Group 3, has been commanded to shutdown with on delay. 0x0174
    06/03/2018 07:13:31 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned off. 0x0135
    06/03/2018 07:13:31 Device UPS: Switched outlet group 2, Outlet Group 2, has been commanded to shutdown with on delay. 0x0174
    06/03/2018 07:13:31 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned off. 0x0135
    06/03/2018 07:13:31 Device UPS: Switched outlet group 1, Outlet Group 1, has been commanded to shutdown with on delay. 0x0174
    06/03/2018 07:13:31 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned off. 0x0135
    06/03/2018 07:13:16 Device UPS: The output power is now turned on. 0x0113
    06/03/2018 07:13:16 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned on. 0x0134
    06/03/2018 07:13:16 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned on. 0x0134
    06/03/2018 07:13:16 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned on. 0x0134
    06/03/2018 07:13:10 Device UPS: The output power is turned off. 0x0114
    06/03/2018 07:13:10 Device UPS: The graceful shutdown period has ended. 0x014F
    06/03/2018 07:13:10 Device UPS: Switched outlet group 3, Outlet Group 3, has been commanded to shutdown with on delay. 0x0174
    06/03/2018 07:13:10 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned off. 0x0135
    06/03/2018 07:13:10 Device UPS: Switched outlet group 2, Outlet Group 2, has been commanded to shutdown with on delay. 0x0174
    06/03/2018 07:13:10 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned off. 0x0135
    06/03/2018 07:13:10 Device UPS: Switched outlet group 1, Outlet Group 1, has been commanded to shutdown with on delay. 0x0174
    06/03/2018 07:13:10 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned off. 0x0135
    06/03/2018 07:13:10 Device UPS: The output power is now turned on. 0x0113
    06/03/2018 07:13:10 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned on. 0x0134
    06/03/2018 07:13:10 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned on. 0x0134
    06/03/2018 07:13:10 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned on. 0x0134
    06/03/2018 07:13:05 Device UPS: The output power is turned off. 0x0114
    06/03/2018 07:13:05 Device UPS: The graceful shutdown period has ended. 0x014F
    06/03/2018 07:13:04 Device UPS: Switched outlet group 3, Outlet Group 3, has been commanded to shutdown with on delay. 0x0174
    06/03/2018 07:13:04 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned off. 0x0135
    06/03/2018 07:13:04 Device UPS: Switched outlet group 2, Outlet Group 2, has been commanded to shutdown with on delay. 0x0174
    06/03/2018 07:13:04 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned off. 0x0135
    06/03/2018 07:13:04 Device UPS: Switched outlet group 1, Outlet Group 1, has been commanded to shutdown with on delay. 0x0174
    06/03/2018 07:13:04 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned off. 0x0135
    06/03/2018 07:12:53 Device UPS: The output power is now turned on. 0x0113
    06/03/2018 07:12:53 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned on. 0x0134
    06/03/2018 07:12:53 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned on. 0x0134
    06/03/2018 07:12:53 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned on. 0x0134
    06/03/2018 07:12:47 Device UPS: The output power is turned off. 0x0114
    06/03/2018 07:12:47 Device UPS: The graceful shutdown period has ended. 0x014F
    06/03/2018 07:12:47 Device UPS: Switched outlet group 3, Outlet Group 3, has been commanded to shutdown with on delay. 0x0174
    06/03/2018 07:12:47 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned off. 0x0135
    06/03/2018 07:12:47 Device UPS: Switched outlet group 2, Outlet Group 2, has been commanded to shutdown with on delay. 0x0174
    06/03/2018 07:12:47 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned off. 0x0135
    06/03/2018 07:12:47 Device UPS: Switched outlet group 1, Outlet Group 1, has been commanded to shutdown with on delay. 0x0174
    06/03/2018 07:12:47 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned off. 0x0135
    06/03/2018 07:12:45 Device UPS: The output power is now turned on. 0x0113
    06/03/2018 07:12:45 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned on. 0x0134
    06/03/2018 07:12:45 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned on. 0x0134
    06/03/2018 07:12:45 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned on. 0x0134
    06/03/2018 07:12:39 Device UPS: The output power is turned off. 0x0114
    06/03/2018 07:12:39 Device UPS: The graceful shutdown period has ended. 0x014F
    06/03/2018 07:12:39 Device UPS: Switched outlet group 3, Outlet Group 3, has been commanded to shutdown with on delay. 0x0174
    06/03/2018 07:12:39 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned off. 0x0135
    06/03/2018 07:12:39 Device UPS: Switched outlet group 2, Outlet Group 2, has been commanded to shutdown with on delay. 0x0174
    06/03/2018 07:12:39 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned off. 0x0135
    06/03/2018 07:12:39 Device UPS: Switched outlet group 1, Outlet Group 1, has been commanded to shutdown with on delay. 0x0174
    06/03/2018 07:12:39 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned off. 0x0135
    06/03/2018 07:12:36 Device UPS: The output power is now turned on. 0x0113
    06/03/2018 07:12:36 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned on. 0x0134
    06/03/2018 07:12:36 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned on. 0x0134
    06/03/2018 07:12:36 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned on. 0x0134
    06/03/2018 07:12:31 Device UPS: The output power is turned off. 0x0114
    06/03/2018 07:12:31 Device UPS: The graceful shutdown period has ended. 0x014F
    06/03/2018 07:12:31 Device UPS: Switched outlet group 3, Outlet Group 3, has been commanded to shutdown with on delay. 0x0174
    06/03/2018 07:12:31 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned off. 0x0135
    06/03/2018 07:12:31 Device UPS: Switched outlet group 2, Outlet Group 2, has been commanded to shutdown with on delay. 0x0174
    06/03/2018 07:12:31 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned off. 0x0135
    06/03/2018 07:12:31 Device UPS: Switched outlet group 1, Outlet Group 1, has been commanded to shutdown with on delay. 0x0174
    06/03/2018 07:12:31 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned off. 0x0135
    06/03/2018 07:12:29 Device UPS: The output power is now turned on. 0x0113
    06/03/2018 07:12:29 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned on. 0x0134
    06/03/2018 07:12:29 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned on. 0x0134
    06/03/2018 07:12:29 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned on. 0x0134
    06/03/2018 07:12:18 Device UPS: The output power is turned off. 0x0114
    06/03/2018 07:12:18 Device UPS: The graceful shutdown period has ended. 0x014F
    06/03/2018 07:12:17 Device UPS: The output power is now turned on. 0x0113
    06/03/2018 07:12:06 Device UPS: The output power is turned off. 0x0114
    06/03/2018 07:12:06 Device UPS: The graceful shutdown period has ended. 0x014F
    06/03/2018 07:12:06 Device UPS: The output power is now turned on. 0x0113
    06/03/2018 07:12:00 Device UPS: The output power is turned off. 0x0114
    06/03/2018 07:12:00 Device UPS: The graceful shutdown period has ended. 0x014F
    06/03/2018 07:11:59 Device UPS: Switched outlet group 3, Outlet Group 3, has been commanded to shutdown with on delay. 0x0174
    06/03/2018 07:11:59 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned off. 0x0135
    06/03/2018 07:11:59 Device UPS: Switched outlet group 2, Outlet Group 2, has been commanded to shutdown with on delay. 0x0174
    06/03/2018 07:11:59 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned off. 0x0135
    06/03/2018 07:11:59 Device UPS: Switched outlet group 1, Outlet Group 1, has been commanded to shutdown with on delay. 0x0174
    06/03/2018 07:11:59 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned off. 0x0135
    06/03/2018 07:11:42 Device UPS: The output power is now turned on. 0x0113
    06/03/2018 07:11:42 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned on. 0x0134
    06/03/2018 07:11:42 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned on. 0x0134
    06/03/2018 07:11:42 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned on. 0x0134
    06/03/2018 07:11:37 Device UPS: The output power is turned off. 0x0114
    06/03/2018 07:11:37 Device UPS: The graceful shutdown period has ended. 0x014F
    06/03/2018 07:11:36 Device UPS: Switched outlet group 3, Outlet Group 3, has been commanded to shutdown with on delay. 0x0174
    06/03/2018 07:11:36 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned off. 0x0135
    06/03/2018 07:11:36 Device UPS: Switched outlet group 2, Outlet Group 2, has been commanded to shutdown with on delay. 0x0174
    06/03/2018 07:11:36 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned off. 0x0135
    06/03/2018 07:11:36 Device UPS: Switched outlet group 1, Outlet Group 1, has been commanded to shutdown with on delay. 0x0174
    06/03/2018 07:11:36 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned off. 0x0135
    06/03/2018 07:11:33 Device UPS: The output power is now turned on. 0x0113
    06/03/2018 07:11:33 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned on. 0x0134
    06/03/2018 07:11:33 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned on. 0x0134
    06/03/2018 07:11:33 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned on. 0x0134
    06/03/2018 07:11:29 Device UPS: The output power is turned off. 0x0114
    06/03/2018 07:11:29 Device UPS: The graceful shutdown period has ended. 0x014F
    06/03/2018 07:11:29 Device UPS: Switched outlet group 3, Outlet Group 3, has been commanded to shutdown with on delay. 0x0174
    06/03/2018 07:11:29 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned off. 0x0135
    06/03/2018 07:11:29 Device UPS: Switched outlet group 2, Outlet Group 2, has been commanded to shutdown with on delay. 0x0174
    06/03/2018 07:11:29 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned off. 0x0135
    06/03/2018 07:11:29 Device UPS: Switched outlet group 1, Outlet Group 1, has been commanded to shutdown with on delay. 0x0174
    06/03/2018 07:11:29 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned off. 0x0135
    06/03/2018 07:11:28 Device UPS: The output power is now turned on. 0x0113
    06/03/2018 07:11:28 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned on. 0x0134
    06/03/2018 07:11:28 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned on. 0x0134
    06/03/2018 07:11:28 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned on. 0x0134
    06/03/2018 07:11:23 Device UPS: The output power is turned off. 0x0114
    06/03/2018 07:11:23 Device UPS: The graceful shutdown period has ended. 0x014F
    06/03/2018 07:11:23 Device UPS: Switched outlet group 3, Outlet Group 3, has been commanded to shutdown with on delay. 0x0174
    06/03/2018 07:11:23 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned off. 0x0135
    06/03/2018 07:11:23 Device UPS: Switched outlet group 2, Outlet Group 2, has been commanded to shutdown with on delay. 0x0174
    06/03/2018 07:11:23 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned off. 0x0135
    06/03/2018 07:11:23 Device UPS: Switched outlet group 1, Outlet Group 1, has been commanded to shutdown with on delay. 0x0174
    06/03/2018 07:11:23 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned off. 0x0135
    06/03/2018 07:11:22 Device UPS: The output power is now turned on. 0x0113
    06/03/2018 07:11:22 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned on. 0x0134
    06/03/2018 07:11:22 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned on. 0x0134
    06/03/2018 07:11:22 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned on. 0x0134
    06/03/2018 07:11:17 Device UPS: The output power is turned off. 0x0114
    06/03/2018 07:11:17 Device UPS: The graceful shutdown period has ended. 0x014F
    06/03/2018 07:11:16 Device UPS: Switched outlet group 3, Outlet Group 3, has been commanded to shutdown with on delay. 0x0174
    06/03/2018 07:11:16 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned off. 0x0135
    06/03/2018 07:11:16 Device UPS: Switched outlet group 2, Outlet Group 2, has been commanded to shutdown with on delay. 0x0174
    06/03/2018 07:11:16 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned off. 0x0135
    06/03/2018 07:11:16 Device UPS: Switched outlet group 1, Outlet Group 1, has been commanded to shutdown with on delay. 0x0174
    06/03/2018 07:11:16 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned off. 0x0135
    06/03/2018 07:11:16 Device UPS: The output power is now turned on. 0x0113
    06/03/2018 07:11:16 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned on. 0x0134
    06/03/2018 07:11:16 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned on. 0x0134
    06/03/2018 07:11:16 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned on. 0x0134
    06/03/2018 07:11:11 Device UPS: The output power is turned off. 0x0114
    06/03/2018 07:11:11 Device UPS: The graceful shutdown period has ended. 0x014F
    06/03/2018 07:11:10 Device UPS: Switched outlet group 3, Outlet Group 3, has been commanded to shutdown with on delay. 0x0174
    06/03/2018 07:11:10 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned off. 0x0135
    06/03/2018 07:11:10 Device UPS: Switched outlet group 2, Outlet Group 2, has been commanded to shutdown with on delay. 0x0174
    06/03/2018 07:11:10 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned off. 0x0135
    06/03/2018 07:11:10 Device UPS: Switched outlet group 1, Outlet Group 1, has been commanded to shutdown with on delay. 0x0174
    06/03/2018 07:11:10 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned off. 0x0135
    06/03/2018 07:11:09 Device UPS: The output power is now turned on. 0x0113
    06/03/2018 07:11:09 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned on. 0x0134
    06/03/2018 07:11:09 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned on. 0x0134
    06/03/2018 07:11:09 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned on. 0x0134
    06/03/2018 07:11:04 Device UPS: The output power is turned off. 0x0114
    06/03/2018 07:11:04 Device UPS: The graceful shutdown period has ended. 0x014F
    06/03/2018 07:11:03 Device UPS: Switched outlet group 3, Outlet Group 3, has been commanded to shutdown with on delay. 0x0174
    06/03/2018 07:11:03 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned off. 0x0135
    06/03/2018 07:11:03 Device UPS: Switched outlet group 2, Outlet Group 2, has been commanded to shutdown with on delay. 0x0174
    06/03/2018 07:11:03 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned off. 0x0135
    06/03/2018 07:11:03 Device UPS: Switched outlet group 1, Outlet Group 1, has been commanded to shutdown with on delay. 0x0174
    06/03/2018 07:11:03 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned off. 0x0135
    06/03/2018 07:11:02 Device UPS: The output power is now turned on. 0x0113
    06/03/2018 07:11:02 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned on. 0x0134
    06/03/2018 07:11:02 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned on. 0x0134
    06/03/2018 07:11:02 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned on. 0x0134
    06/03/2018 07:10:57 Device UPS: The output power is turned off. 0x0114
    06/03/2018 07:10:57 Device UPS: The graceful shutdown period has ended. 0x014F
    06/03/2018 07:10:57 Device UPS: Switched outlet group 3, Outlet Group 3, has been commanded to shutdown with on delay. 0x0174
    06/03/2018 07:10:57 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned off. 0x0135
    06/03/2018 07:10:57 Device UPS: Switched outlet group 2, Outlet Group 2, has been commanded to shutdown with on delay. 0x0174
    06/03/2018 07:10:57 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned off. 0x0135
    06/03/2018 07:10:57 Device UPS: Switched outlet group 1, Outlet Group 1, has been commanded to shutdown with on delay. 0x0174
    06/03/2018 07:10:57 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned off. 0x0135
    06/03/2018 07:10:56 Device UPS: The output power is now turned on. 0x0113
    06/03/2018 07:10:56 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned on. 0x0134
    06/03/2018 07:10:56 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned on. 0x0134
    06/03/2018 07:10:56 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned on. 0x0134
    06/03/2018 07:10:51 Device UPS: The output power is turned off. 0x0114
    06/03/2018 07:10:51 Device UPS: The graceful shutdown period has ended. 0x014F
    06/03/2018 07:10:50 Device UPS: The output power is now turned on. 0x0113
    06/03/2018 07:10:45 Device UPS: The output power is turned off. 0x0114
    06/03/2018 07:10:45 Device UPS: The graceful shutdown period has ended. 0x014F
    06/03/2018 07:10:44 Device UPS: The output power is now turned on. 0x0113
    06/03/2018 07:10:39 Device UPS: The output power is turned off. 0x0114
    06/03/2018 07:10:39 Device UPS: The graceful shutdown period has ended. 0x014F
    06/03/2018 07:10:38 Device UPS: Switched outlet group 3, Outlet Group 3, has been commanded to shutdown with on delay. 0x0174
    06/03/2018 07:10:38 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned off. 0x0135
    06/03/2018 07:10:38 Device UPS: Switched outlet group 2, Outlet Group 2, has been commanded to shutdown with on delay. 0x0174
    06/03/2018 07:10:38 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned off. 0x0135
    06/03/2018 07:10:38 Device UPS: Switched outlet group 1, Outlet Group 1, has been commanded to shutdown with on delay. 0x0174
    06/03/2018 07:10:38 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned off. 0x0135
    06/03/2018 07:10:36 Device UPS: The output power is now turned on. 0x0113
    06/03/2018 07:10:36 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned on. 0x0134
    06/03/2018 07:10:36 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned on. 0x0134
    06/03/2018 07:10:36 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned on. 0x0134
    06/03/2018 07:10:30 Device UPS: The output power is turned off. 0x0114
    06/03/2018 07:10:30 Device UPS: The graceful shutdown period has ended. 0x014F
    06/03/2018 07:10:30 Device UPS: Switched outlet group 3, Outlet Group 3, has been commanded to shutdown with on delay. 0x0174
    06/03/2018 07:10:30 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned off. 0x0135
    06/03/2018 07:10:30 Device UPS: Switched outlet group 2, Outlet Group 2, has been commanded to shutdown with on delay. 0x0174
    06/03/2018 07:10:30 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned off. 0x0135
    06/03/2018 07:10:30 Device UPS: Switched outlet group 1, Outlet Group 1, has been commanded to shutdown with on delay. 0x0174
    06/03/2018 07:10:30 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned off. 0x0135
    06/03/2018 07:10:29 Device UPS: The output power is now turned on. 0x0113
    06/03/2018 07:10:29 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned on. 0x0134
    06/03/2018 07:10:29 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned on. 0x0134
    06/03/2018 07:10:29 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned on. 0x0134
    06/03/2018 07:10:24 Device UPS: The output power is turned off. 0x0114
    06/03/2018 07:10:24 Device UPS: The graceful shutdown period has ended. 0x014F
    06/03/2018 07:10:23 Device UPS: The output power is now turned on. 0x0113
    06/03/2018 07:10:18 Device UPS: The output power is turned off. 0x0114
    06/03/2018 07:10:18 Device UPS: The graceful shutdown period has ended. 0x014F
    06/03/2018 07:10:17 Device UPS: The output power is now turned on. 0x0113
    06/03/2018 07:10:11 Device UPS: The output power is turned off. 0x0114
    06/03/2018 07:10:11 Device UPS: The graceful shutdown period has ended. 0x014F
    06/03/2018 07:10:11 Device UPS: Switched outlet group 3, Outlet Group 3, has been commanded to shutdown with on delay. 0x0174
    06/03/2018 07:10:11 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned off. 0x0135
    06/03/2018 07:10:11 Device UPS: Switched outlet group 2, Outlet Group 2, has been commanded to shutdown with on delay. 0x0174
    06/03/2018 07:10:11 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned off. 0x0135
    06/03/2018 07:10:11 Device UPS: Switched outlet group 1, Outlet Group 1, has been commanded to shutdown with on delay. 0x0174
    06/03/2018 07:10:11 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned off. 0x0135
    06/03/2018 07:10:10 Device UPS: The output power is now turned on. 0x0113
    06/03/2018 07:10:10 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned on. 0x0134
    06/03/2018 07:10:10 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned on. 0x0134
    06/03/2018 07:10:10 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned on. 0x0134
    06/03/2018 07:10:04 Device UPS: The output power is turned off. 0x0114
    06/03/2018 07:10:04 Device UPS: The graceful shutdown period has ended. 0x014F
    06/03/2018 07:10:04 Device UPS: The output power is now turned on. 0x0113
    06/03/2018 07:09:59 Device UPS: The output power is turned off. 0x0114
    06/03/2018 07:09:59 Device UPS: The graceful shutdown period has ended. 0x014F
    06/03/2018 07:09:59 Device UPS: Switched outlet group 3, Outlet Group 3, has been commanded to shutdown with on delay. 0x0174
    06/03/2018 07:09:59 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned off. 0x0135
    06/03/2018 07:09:58 Device UPS: Switched outlet group 2, Outlet Group 2, has been commanded to shutdown with on delay. 0x0174
    06/03/2018 07:09:58 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned off. 0x0135
    06/03/2018 07:09:58 Device UPS: Switched outlet group 1, Outlet Group 1, has been commanded to shutdown with on delay. 0x0174
    06/03/2018 07:09:58 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned off. 0x0135
    06/03/2018 07:09:57 Device UPS: The output power is now turned on. 0x0113
    06/03/2018 07:09:57 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned on. 0x0134
    06/03/2018 07:09:57 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned on. 0x0134
    06/03/2018 07:09:57 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned on. 0x0134
    06/03/2018 07:09:52 Device UPS: The output power is turned off. 0x0114
    06/03/2018 07:09:52 Device UPS: The graceful shutdown period has ended. 0x014F
    06/03/2018 07:09:51 Device UPS: Switched outlet group 3, Outlet Group 3, has been commanded to shutdown with on delay. 0x0174
    06/03/2018 07:09:51 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned off. 0x0135
    06/03/2018 07:09:51 Device UPS: Switched outlet group 2, Outlet Group 2, has been commanded to shutdown with on delay. 0x0174
    06/03/2018 07:09:51 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned off. 0x0135
    06/03/2018 07:09:51 Device UPS: Switched outlet group 1, Outlet Group 1, has been commanded to shutdown with on delay. 0x0174
    06/03/2018 07:09:51 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned off. 0x0135
    06/03/2018 07:09:51 Device UPS: The output power is now turned on. 0x0113
    06/03/2018 07:09:51 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned on. 0x0134
    06/03/2018 07:09:51 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned on. 0x0134
    06/03/2018 07:09:51 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned on. 0x0134
    06/03/2018 07:09:46 Device UPS: The output power is turned off. 0x0114
    -----------
    I thought that was strange, I couldn't find any explanation for this.  Then this evening, it did it again!
    ----
    06/03/2018 22:42:38 apc Web user 'apc' logged in from 10.5.0.196 [10.5.0.196]. 0x0015
    06/03/2018 22:37:02 Device UPS: The output power is now turned on. 0x0113
    06/03/2018 22:37:02 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned on. 0x0134
    06/03/2018 22:37:02 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned on. 0x0134
    06/03/2018 22:37:02 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned on. 0x0134
    06/03/2018 22:36:57 Device UPS: The output power is turned off. 0x0114
    06/03/2018 22:36:57 Device UPS: The graceful shutdown period has ended. 0x014F
    06/03/2018 22:36:56 Device UPS: Switched outlet group 3, Outlet Group 3, has been commanded to shutdown with on delay. 0x0174
    06/03/2018 22:36:56 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned off. 0x0135
    06/03/2018 22:36:56 Device UPS: Switched outlet group 2, Outlet Group 2, has been commanded to shutdown with on delay. 0x0174
    06/03/2018 22:36:56 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned off. 0x0135
    06/03/2018 22:36:56 Device UPS: Switched outlet group 1, Outlet Group 1, has been commanded to shutdown with on delay. 0x0174
    06/03/2018 22:36:56 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned off. 0x0135
    --
    There appears to be nothing in the UPS Fault logs.  The UPS Transition Logs do show distorted input earlier, but not during the recent shutdown.
    1 06/03/2018 04:47:54.000 3 distorted input
    2 06/03/2018 09:01:48.000 3 distorted input
    3 06/03/2018 07:25:19.000 3 distorted input
    4 06/03/2018 07:18:30.000 3 distorted input
    5 06/03/2018 07:18:22.000 3 distorted input
    6 06/03/2018 07:17:54.000 3 distorted input
    7 06/03/2018 07:17:10.000 3 distorted input
    8 06/03/2018 07:16:55.000 3 distorted input
    9 06/03/2018 07:15:12.000 3 distorted input
    10 06/03/2018 07:15:05.000 3 distorted input
    Any ideas?  I'm worried it's just going to randomly shut all the outlets down again.
    Matt
  • liamg
    Liam
    =S= Representative
    Liam 16 days ago (in response to Matt)

    Hi Matt -

    What exactly is connected to the UPS? Could you attach the data logs?

    You may find that lowering the sensitivty setting of the UPS will reduce the instances of switching to battery due to input distortion.  this can be done via the LCD screen, Network Management Card, or Powerchute Business Edition.

    Thanks

    Liam

     

  • Farmhouse1904
    Matt
    Novice Novice
    Matt 16 days ago (in response to Liam)

    Thanks for the reply Liam.  I have attached the data log.

    Do you recommend LOW or REDUCED for Sensitivity? I'm currently on Normal. What are the dangers in doing this?

    After I posted last night, I went ahead and did the firmware update to 9.9 and the Network Card up to 6.5.6 (it was on 9.1 and 6.5.0).

    I have a variety of equipment attached including:

    A Dell T320 Server, 2 Netgear GS724Tv4 switches, a Synology 916+ NAS, an old Netgear ReadyNAS PRO 6, a Ubiquiti EdgeRouter Lite, a Comcast cable modem/gateway and an Apple Airport Extreme.

    I believe that is about everything attached.  I'll take another peek and make sure I didn't miss anything.

    I did open a ticket with support.  They told me to power every down, unplug everything from the ups, disconnect the batteries, then reconnect everything and power it backup on.  They said this would reset the CPU in the UPS?

    Matt

    Attachments
  • liamg
    Liam
    =S= Representative
    Liam 14 days ago (in response to Matt)

    Hi Matt - 

    I would probably start with "Reduced" and keep an eye on it. If the unit keeps switching to battery, then go with "Low". The tradeoff is that your transfer time (the brief moment when there is no output voltage from the UPS) is extended. Most IT equipment has no problem with this, but occasionally you will find high powered servers that do not like the transfer time. In these (uncommon) situations where the load cannot handle the extended transfer time and the input power requires lower sensitivity the only real option is a Double Online Conversion UPS like our SRT models. This is not common however, and I would not anticipate that you will see any issues.

    thanks

    Liam

  • Farmhouse1904
    Matt
    Novice Novice
    Matt 14 days ago (in response to Liam)

    Thanks Liam.

    Out of curiosity, was there anything of interest in the UPS data log?  Anything that I should be worried about or have checked?

    Also, do you think I should bother doing the "cpu reset", basically shut everything down, unplug all devices, disconnect the batteries, and reconnect and power up?  Is there value in doing that?

    The problem has not happened again since I did the firmware updates.

    I thought about a true-online UPS, but that is a lot more expensive of course.  I've always been a bit confused on this because some other competitors, like MinuteMan, offer "true" online UPS at a much lower price.  But I've always bought APC so I'm leery about going anywhere else.

    I know I'm getting a little off topic here, but how does this relate to what I see marketed as a "true sine-wave" UPS?  I see that talked about a lot too.  

    Realistically, should all the equipment I listed be able to handle the transfer time w/o issue?  Or is anything I listed more sensitive?

    Thanks again.

    Matt

  • liamg
    Liam
    =S= Representative
    Liam 14 days ago (in response to Matt)

    Hi Matt - 

    Everything looked fine in the data logs. Frequency seemed slightly off, but voltage was solid. This leads me to believe the issues you were seeing were related to THD or some instability in the utility power. If the issue has not returned, it's possible that it was just a temporary power disturbance and that there is no need to adjust the unit.  If you do adjust the unit, I don't think your load will have any issue with the transfer time. I don't think there is any need to perform the "brain dead" procedure that tech support recommended. 

    The Online units do offer tighter power regulation and no transfer time. The power quality is definitely the best that can be had, and they are better at dealing with really poor quality input power. That being said, they are expensive and fairly complex. If there is not a pressing need for one, I really think that a standard Line Interactive Smart-UPS is probably the best bet for most applications in this size range. They're relatively inexpensive, reliable, and efficient. All Smart-UPS output a pure sine wave and are appropriate for IT environments. Given your application, I think your SMX1500 is probably the best tool for the job.

    Hope this helps,

    Liam

    T

  • Farmhouse1904
    Matt
    Novice Novice
    Matt 14 days ago (in response to Liam)

    Thanks again Liam for your informative replies!

    I've been an APC user for well over 20 years and I've been very happy with the products, so it's good to hear you think we have the right equipment for this site.

    The Frequency being off in the data logs, is that something I should ask the local utility (DTE Energy) about? 

    Could this be related to a problematic ground at all? We had some issues with Comcast last year and Comcast thought maybe our ground was suspect, but it appears solid to me (but I'm not an electrician).  I did have DTE check at the pole a year ago and they did replace some old taps, but otherwise said everything looked fine.

    Matt

  • Page 1 of 1 (7 items)
Choose your language:  
powered by Communifire
Version 5.2.6420.11692