SMT 1500

Discussion in Smart-UPS & Symmetra LX / RM started by Michele , 16 days ago
Login to follow, share, and participate in this space.
Not a member?Join now
  • MicaAPC
    Michele
    Novice Novice
    Michele 16 days ago
    Good morning,
    We are 3 IT companies and we often sell this product:
    APC Back-UPS BX
    We work perfectly with this product.
    Now we need superior products.
    So we bought this:
    APC Smart-UPS - Uninterruptible Power Supply (UPS) 750VA Model Tower - SMT750I
    and here the problems have arrived for our technicians.
    Let's start with the first big problem:
    Email notification. We set this configuration
    (see Attachment)
    if the line goes away to the customer we absolutely do not receive anything ...
    we do not even see the panel to send a test email to test the settings
    We await yours
    Attachments
  • wpasquil
    Bill
    =S= Representative
    Bill 16 days ago (in response to Michele)

    Hi,

    If you want to send e-mail from PowerChute Business Edition to smtp.gmail.com you will first need to upgrade PowerChute to version 9.5. See Schneider Electric FAQ FA249593

    The port for smtp.gmail.com is 465 Use SSL

    We do not offer a test button at this time. It will be added as a feature in a future release. For now to test e-mail you can configure the software to send e-mail when a self-test is run. The through PowerChute trigger a self-test. To trigger a self-test go to Smart-UPS 750 - Diagnostics 

    You will find information on e-mails sent in the pcbe.log file. The default path to the log for Windows is C:\Program Files (x86)\APC\PowerChute Business Edition\agent\log

  • MicaAPC
    Michele
    Novice Novice
    Michele 11 days ago (in response to Bill)
    Many thanks for the reply
    We did the powerchute update
    We have changed the parameters (see screen)
    We did the test (SELF TEST + TEST ALARM)
    No email arrived ...
    we are waiting for you
    thank you
  • MicaAPC
    Michele
    Novice Novice
    Michele 11 days ago (in response to Michele)

    Attach log

    Attachments
  • wpasquil
    Bill
    =S= Representative
    Bill 11 days ago (in response to Michele)

    Hi,

    The log show an issue resolving the SMTP host 

    2018-05-12 12:21:12,464 [SMTPMailWorker] WARN  - [SMTPMailer.SMTPMailWorker] SMTPMailConfigException :javax.mail.MessagingException: Unknown SMTP host: smtp.gmail.com;

      nested exception is:

                    java.net.UnknownHostException: smtp.gmail.com

    2018-05-12 12:21:12,464 [SMTPMailWorker] WARN  - [SMTPMailer.SMTPMailWorker] com.apcc.m11.components.SMTPMailer.SMTPMailConfigException: javax.mail.MessagingException: Unknown SMTP host: smtp.gmail.com;

      nested exception is:

                    java.net.UnknownHostException: smtp.gmail.com

  • MicaAPC
    Michele
    Novice Novice
    Michele 7 days ago (in response to Bill)

    does your message mean that it is correctly configured to send emails right?

    email has arrived .... but only when I unplugged the usb cable

    _________________________

    Let's move on to the second question

    We must understand perfectly the logics of shutdown of the APC, because we will install them on industrial servers.

    We need the APC to shut down the server it is connected to (Windows Server 2016) 3 minutes before it runs out.

    Do you confirm the screenshot?

    Another thing ... is it possible to test the auto switch-off procedure?

    Thank you

    Attachments
  • wpasquil
    Bill
    =S= Representative
    Bill 4 days ago (in response to Michele)

    Hi,

    I The screenshot show that the OS needs 3 minutes to power down. I recommend increasing the runtime limit to 5 minutes to allow a 2 minute buffer. Also you should add a minimum battery return requirement. The requirement should be determined by the amount of time the system needs to boot and to power down. 

    In the above example I add a 7 minute delay. I based this on the system needing 2 minutes to boot, 3 minutes to power down and added a 2 minute buffer. The reasoning to allow the system to safely boot up and power down in the event there is a power outage prior to the UPS fully charging. 