APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:31 AM . Last Modified: 2024-03-18 01:27 AM
Hello,
I recently acquired a used SMT-1000 with a date of manufacture of 08/2011. Presently, the unit is on the UPS 06.5 (ID18) firmware. I have looked into the various processes of updating it's firmware, however I still have some questions.
According to the firmware revision matrix found in this how to article, the most up to date firmware version I could put on the unit is UPS 7.1. However, the article that describes updating the UPS firmware via the NMC shows that the correct firmware file for my unit would install UPS 9.4. In addition, when I look at the readme file for this update it does not show the list of release notes beyond UPS 09.3.
So, I guess my question is how can I tell what firmware my unit is actually compatible with? Is there a reason that the update wizard article states that it will only update my unit to UPS 0.7.1, despite the NMC method article saying that I can update to UPS 0.9.4?
Thanks in advance!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:31 AM . Last Modified: 2024-03-18 01:27 AM
Hi Matt -
The only thing that matters in selecting the firmware is the ID#. Are you absolutely certain that your unit is 18 and not 17? The matrix in the article from the Firmware Upgrade Wizard is assuming that if your unit has UPS FW less than 8.0, it is an ID17 unit.
Our recommendation for upgrading UPS FW is to use the Firmware Upgrade Wizard (via Serial) if at all possible. It includes additional system checks that are not possible when using the Network Management Card. Furthermore, on an older UPS that is out of warranty I probably wouldn't upgrade the firmware unless you are experiencing an issue of some sort. If the unit is not performing as expected, then by all means upgrade the FW, but beyond that I tend to take an "If it ain't broke, don't fix it" approach. You can use the Network Interface for the UPS while you are awaiting batteries, but I would not upgrade the firmware until you have new batteries installed in the unit.
We have release notes for many of the images, but not all. All new releases moving forwards will have release notes attached. For the FW revs that have release notes you will find them bundled with the .enc files. For UPS ID 18 image the changes are as follows:
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:31 AM . Last Modified: 2024-03-18 01:27 AM
The ID is the only thing that matters. There second document shows an ID 18 UPS 9.4 file so your UPS can be upgraded to 9.4. Perhaps the second document is newer. You can also "unzip" the firmware upgrade wizard and get all the files and pick the ID 18 one.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:31 AM . Last Modified: 2024-03-18 01:27 AM
So I guess my next question is where I can find all of the changes between UPS 6.5 and the most current firmware.
Also, is there any harm in updating using the NIC without any batteries installed? I am presently waiting for a set to be ordered.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:31 AM . Last Modified: 2024-03-18 01:27 AM
Hi Matt -
The only thing that matters in selecting the firmware is the ID#. Are you absolutely certain that your unit is 18 and not 17? The matrix in the article from the Firmware Upgrade Wizard is assuming that if your unit has UPS FW less than 8.0, it is an ID17 unit.
Our recommendation for upgrading UPS FW is to use the Firmware Upgrade Wizard (via Serial) if at all possible. It includes additional system checks that are not possible when using the Network Management Card. Furthermore, on an older UPS that is out of warranty I probably wouldn't upgrade the firmware unless you are experiencing an issue of some sort. If the unit is not performing as expected, then by all means upgrade the FW, but beyond that I tend to take an "If it ain't broke, don't fix it" approach. You can use the Network Interface for the UPS while you are awaiting batteries, but I would not upgrade the firmware until you have new batteries installed in the unit.
We have release notes for many of the images, but not all. All new releases moving forwards will have release notes attached. For the FW revs that have release notes you will find them bundled with the .enc files. For UPS ID 18 image the changes are as follows:
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.