SMART-UPS 2200 - Warning State: Replace battery

Discussion in Smart-UPS & Symmetra LX / RM started by Suhail , 8 days ago
Login to follow, share, and participate in this space.
Not a member?Join now
  • MSR175
    Suhail
    New Member New Member
    Suhail 8 days ago

    Hello All, 

    i am having an issue with newly installed APC smart UPS 2200VA. After installing the unit and adding load on it displayed an error on the screen Warning State: Replace battery and continuously giving me alarms. Could some one help me in fixing the issue. Have i missed something in enabling in the UPS or the battery is already defectedError message defected. 

  • MarkC
    Mark
    Apprentice Apprentice
    Mark 6 days ago (in response to Suhail)

    Appears to be a SMT-2200RM unit?  What are the first 4 digits of the serial numbers on the UPS and also the battery pack?  I've seen "new" in-box units being sold that are over 7 years old - the batteries will not be any good.